Hi all - new to the forum and had a (hopefully) straightforward question.

I recently had some professional work done and contractor put in a new vent through the roof, and installed a p-trap in the wall, and then 90'd to what will be a bathroom sink. Further down that pipe I have a utility sink utilizing that same p-trap.

With the p trap in the wall do I still need to have an additional p trap under each sink?

Rough sketch attached for clarity

Thanks
 
Last edited by a moderator:

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
WHO would ever put a "running trap" inside a wall? That is one of the worst ideas ever. It is NOT permitted, and even if it were, it would be a bad idea. You CANNOT have any additional traps under the sinks if you want them to drain.
 

Harris

New Member
Messages
6
Reaction score
2
Points
3
Location
Minnesota
The walls are currently unfinished, so it sounds like an easy fix is to remove the p trap in the wall and just let the traps from the sinks do their thing?
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
plumbing-goofy.jpg


Normally the lav has a higher drain anyway, so I would run a trap arm over to the laundry tray and vent that back to the stack at 42"
Then I would stack a santee over that and arm over for the lav.

Back to back p-traps are often done this way too.

double_lav_rough_1.jpg
 
Last edited:

WorthFlorida

Clinical Trail 5th session completed 4/24/24.
Messages
5,763
Solutions
1
Reaction score
998
Points
113
Location
Orlando, Florida
The only p traps that can be hidden is one for a washing machine drain (in the wall 6-18" from the floor), and the other is a bathtub and shower drains below the floor level.
 

Harris

New Member
Messages
6
Reaction score
2
Points
3
Location
Minnesota
I've finally found some time to fix these traps and had a couple questions on material. The attached picture hopefully provides clarity.

Hopefully the rubber couplings are OK for splicing into the existing vent, but my main question is can I use a horizontal Santee to vent upwards or do I need to use a wye plus a 45 coupling to make the 90 degree turn up.

Thanks again.
 

Attachments

  • 20190613_083609.jpg
    20190613_083609.jpg
    45.2 KB · Views: 190

Reach4

Well-Known Member
Messages
38,899
Reaction score
4,436
Points
113
Location
IL
"Rubber couplings" should be shielded couplings. Dish detergent makes a nice lube for putting them on.

Thing circled in red should not be a santee. It can be wye plus a 45 coupling for sure.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
Code for the fitting on it's back is a wye or combo.
A santee works though. It just won't pass inspection where I'm at.

mission_bandseal.jpg


These with the metal wrap prevent the pipes from shifting. The all rubber couplings aren't code approved.
 