Advice on drain design

Users who are viewing this thread

Olmedo

New Member
Messages
5
Reaction score
0
Points
1
Location
Point Roberts, WA
pmVfM9r9p

I'm asking about the end of the drain line at the bottom center of the design. Am I able to use a 3" Sanitary Combo and then reduce the drain to 1 1/2" for the lav drain? That is the only fixture that will drain there. Or do I have to run the 3" line above the cleanout before reducing? Code is UPC with no applicable amendments. Thank you
 
Last edited:

Plumber01

In the Trades
Messages
108
Reaction score
17
Points
18
Location
Washington
You can eliminate the lav drain altogether.

Use the toilet vent for the lav drain. 3" Santee for a cleanout, 3x2" bushing in the top of the Santee, 2x1.5" Santee for the lav drain, 2" vent through the roof.
 

Olmedo

New Member
Messages
5
Reaction score
0
Points
1
Location
Point Roberts, WA
pm0YX65xp
pouMcIGFp

So it would look like this then? Seemed like it was a much cleaner run the other way. Also, the cleanout was hidden inside the lav cabinet and now it's visible between the toilet and lav.
 