Adding electrical outlet in pump house

Users who are viewing this thread

rnparamedic69

Member
Messages
31
Reaction score
0
Points
6
Location
South carolina
I’m wanting to add an electrical outlet in my well pump house. The well pump is 220v and fed from 30amp breaker in the house. Wire is 10/3.
Should I bring wire from house into a junction box, then tie one “hot” leg,neutral,and ground to electrical outlet, AS WELL AS, tying into well pump as it is wired now???
Or, could I just come off the contacts from the well pump for the electrical outlet??
Whichever would be safest and best for the well pump.
Thanks
 

Reach4

Well-Known Member
Messages
38,922
Reaction score
4,447
Points
113
Location
IL
You want to put in a small sub panel in the pump house. The sub panel will not have a main breaker. Feed the breaker panel with the 30 amp line from the house. Put a 25 amp 2-pole breaker in for the well pump. Put in one (or two side-by-side) 15 amp 1-pole breakers into the panel, and feed 120 volt loads. Maybe add a lighting fixture while you are at it.

The outlets should be GFCI.

If I followed previous posts correctly, you are supposed to add a ground rod for the ground in addition to the ground wire from the house. I am not an electrician.
 
Last edited:

rnparamedic69

Member
Messages
31
Reaction score
0
Points
6
Location
South carolina
You want to put in a small sub panel in the pump house. The sub panel will not have a main breaker. Feed the breaker panel with the 30 amp line from the house. Put a 25 amp 2-pole breaker in for the well pump. Put in one (or two side-by-side) 15 amp 3-pole breakers into the panel, and feed 120 volt loads. Maybe add a lighting fixture while you are at it.

The outlets should be GFCI.

If I followed previous posts correctly, you are supposed to add a ground rod for the ground in addition to the ground wire from the house. I am not an electrician.
That’s an even better plan. Room to add on more loads if needed. Thanks
 