4 wire submersible pump

Users who are viewing this thread

david gosnell

New Member
Messages
1
Reaction score
0
Points
1
Location
Hephzibah, GA
i bought a 4 wire submersible pump for my well before i realized my well is a 3 wire controlled by a pressure switch can i still use the 4 wire pump without the neutral wire
 

Reach4

Well-Known Member
Messages
38,896
Reaction score
4,436
Points
113
Location
IL
i bought a 4 wire submersible pump for my well before i realized my well is a 3 wire controlled by a pressure switch can i still use the 4 wire pump without the neutral wire
  1. Are the wires on your new pump red, black, yellow and green?
  2. Do you have a control box between the pressure switch and the pump?
  3. Is your pump powered by a 240 volt circuit?
If yes, yes and yes, the green wire is the "ground" which is wired to the pump case. If that wire is not run out to the pump, you can just not use that.

If the answers are not all yes, tell us what you have.
 

Craigpump

In the Trades
Messages
2,436
Reaction score
158
Points
63
Location
Connecticut
You can if you get a control box that matches the motor. However, using only three wires means it won't be properly grounded, bonded or up to current code. In addition, some say that leaving the ground wire from the motor unsealed will allow water to wick into the pigtail socket and cause dead shorts to ground.

Just because you can doesn't mean you should.
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
You can if you get a control box that matches the motor. However, using only three wires means it won't be properly grounded, bonded or up to current code. In addition, some say that leaving the ground wire from the motor unsealed will allow water to wick into the pigtail socket and cause dead shorts to ground.

Just because you can doesn't mean you should.

100 years of pumps with either just 2 wires or 3 wires and a control box. That new ground wire is some over educated, under experienced "engineers" idea to waste a few more thousand tons of copper a year. When I cut off the irrelevant ground wire, I rubber tape it and top everything with Scotch 33. Soon as someone can give a detailed answer what in hell a ground wire does for a pump a few hundred feet under water, I'll use it.
 

Craigpump

In the Trades
Messages
2,436
Reaction score
158
Points
63
Location
Connecticut
100 years of pumps with either just 2 wires or 3 wires and a control box. That new ground wire is some over educated, under experienced "engineers" idea to waste a few more thousand tons of copper a year. When I cut off the irrelevant ground wire, I rubber tape it and top everything with Scotch 33. Soon as someone can give a detailed answer what in hell a ground wire does for a pump a few hundred feet under water, I'll use it.

We do tons of well inspections for real estate transactions every year, one of the biggest violations we see are ungrounded/bonded pumps, well caps & steel casings.

I bet you don't like those new fangled GFCI outlets either.....
 

Reach4

Well-Known Member
Messages
38,896
Reaction score
4,436
Points
113
Location
IL
I bet you don't like those new fangled GFCI outlets either.....
Are you planning to put GFCI breakers powering submersible pumps soon? :rolleyes: I certainly would not want my basement sump pump powered by a GFCI, although I know it is required some places.
 

Craigpump

In the Trades
Messages
2,436
Reaction score
158
Points
63
Location
Connecticut
Are you planning to put GFCI breakers powering submersible pumps soon? :rolleyes: I certainly would not want my basement sump pump powered by a GFCI, although I know it is required some places.


No, of course not.

If you were to see some of the horrible pump installs we see with poorly spliced wire, old chafed wire & bare wires under well caps due to rodents you would know why having a properly grounded and bonded submersible pump system makes perfect sense.
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
We do tons of well inspections for real estate transactions every year, one of the biggest violations we see are ungrounded/bonded pumps, well caps & steel casings.

I bet you don't like those new fangled GFCI outlets either.....

I like gfci's when they work, dependant on what a 14 year old china girl' mood was that day. I hate the size - when a tiny chip can hold 1TB of information, gfi's are like a pack of cigarettes. Trying to pack one into a normal box is a hazard in itself, especially if it is downfeeding. But a gfi in your bath and kitchen has nothing to do at all with a well that gets visited -maybe- a few times a year.

I know there are tons of rats nest wiring in pump houses. Got one myself that I did 40 years ago. With poly pipe casing and downpipe and even abs well caps nowadays that ground wire does nothing. If you have steel, run a ground to the cap or casing. But even in that case, if a wire rubs bare on the metal cap or casing, its going to blow the breaker or the pump. And that is with or without a ground to the cap and casing.

So I am still waiting for the exact explanation of what that ground wire on the pump does. I think a lot of people are too.
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
No, of course not.

If you were to see some of the horrible pump installs we see with poorly spliced wire, old chafed wire & bare wires under well caps due to rodents you would know why having a properly grounded and bonded submersible pump system makes perfect sense.

I don't think rats get under the well cap, and they don't eat Al or steel flex or water tite flex that should be going to the well. The guy that has romex going to the well cap with or without a ground already has broken code and common sense. I hate rats!
 

Craigpump

In the Trades
Messages
2,436
Reaction score
158
Points
63
Location
Connecticut
So you've never seen mice living in a well? Most of the time we see them living under the flat 4 bolt Campbell or the domed Monitor caps. Those caps had gaps just big enough for mice to get through. Mice love plastic insulation.
 

Attachments

  • image.jpeg
    image.jpeg
    94.4 KB · Views: 1,082
  • image.jpeg
    image.jpeg
    68.9 KB · Views: 639

Texas Wellman

In the Trades
Messages
1,035
Reaction score
59
Points
48
Location
SE Texas-Coastal
I'm in the 4 wire is a good deal camp. In the 90's before all 3-wires were grounded we were routinely shocked or received a little current when testing the water coming straight out of the pump. Ever since they added the ground wire the shocking stopped. I think it's a big improvement.
 