Quick question - is it a code violation to use a 2-in p trap for a 1 1/2-in tub drain?
Thanks,
Neil
Thanks,
Neil
Thanks Terry - I thought it okay, then did it, then doubted myself. As always, I really appreciate you and all of the contributors here! Have a great night!No, you can use either the 1.5" or the 2.0" trap.
After the vent, it's 2" anyway. Some plumbers like having the 2" for future snaking.
No, you can use either the 1.5" or the 2.0" trap.
After the vent, it's 2" anyway. Some plumbers like having the 2" for future snaking.
Terry - I've only partially plumbed it. I won't get back up there until Saturday morning, but can take some pictures then. I can explain here though, to accompany the picture:Neil,
Is this already plumbed? If so, can you post a picture so I can see better what you have.
The trap arm for the tub should come off on the horizontal from the 3" with a wye or combo.
the vent fitting on it's back is a combo or wye fitting.
Your bath tub trap arm needs to comply with the "trap weir rule," which limits the fall of the fixture drain between the trap outlet and the vent connection to one pipe diameter. For your horizontal wet vent of the bathtub, the vent connection is the wye shown, probably more specifically the point where the branch inlet and the straight inlet join in the body of the wye.- The tub trap arm is a wye and is tilted up around 45. It is a sort of a strange joist situation, but I think I can change it to horizontal (plus 1/4" per foot) if I need to.
Guys - thank you, again, for taking your time to help guide me.
I'll cut out the section with the Wye and put a new on in, turned horizontal, and I'll re-do the trap to make sure that it can properly use the 3" horizontal pipe to wet vent. If I fully understand, I just need to be sure that the p-trap outlet can breath using the air space in the 3" horizontal to reach the vent.
Since Virginia uses IPC, am I okay to leave the santee for the vent?
Thanks again,
Neil
I guess so, in the sense that the air space at the top of the 3" horizontal has to be able to reach the p-trap without the possibility of the trap arm being fully blocked by water. So once you turn your wye horizontal (2% slope on branch inlet), the fall from the p-trap outlet to the wye branch inlet can't exceed one pipe diameter (2" for a 2" p-trap).If I fully understand, I just need to be sure that the p-trap outlet can breath using the air space in the 3" horizontal to reach the vent.
In this case, I think I'll leave it alone. For future reference, though, I think I'll follow your lead and leave santees out of this part of the vent system, just to avoid potential issues. Thank you!I believe santee on back is fine there Neil even though its so wrong to me ha ha not a ton of major differances in our code but that is one. Though
I was taught to use santees that way and found out about 3 years in Id been taught wrong we used to do it anyway. but last 30 years I changed my ways and never put santee on back anymore
Thanks Wayne - I appreciate the way you described it and now better understand how the vent serves the trap and also why a santee would be needed to serve a trap tie in to vertical, instead of a wye.I guess so, in the sense that the air space at the top of the 3" horizontal has to be able to reach the p-trap without the possibility of the trap arm being fully blocked by water. So once you turn your wye horizontal (2% slope on branch inlet), the fall from the p-trap outlet to the wye branch inlet can't exceed one pipe diameter (2" for a 2" p-trap).
Cheers, Wayne