1985 Electrical Code, Bathroom Circuit Amperage in Georgia

Users who are viewing this thread

Dr.Lightning

New Member
Messages
1
Reaction score
0
Points
0
Location
Georgia
In Georgia, I have a rental house built in 1985. At that time, what was code for the amperage of the circuit serving the bathroom? This house has a single 15A breaker for a circuit serving both the master and adjacent guest bathroom, each a full bathroom. I know that code requires a 20A circuit now, but what about back then? (Tenant's 2000W hair dryer plus bright bathroom lights consume 14.7+3.8=18.5A and trip the breaker after a few minutes. No halogen bulbs available for light fixture, although that wouldn't matter anyway with the hair dryer drawing 14.7A and randomly 15.1A on my clamp-on meter.)
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
22
Points
38
Location
North Carolina
In 1984 the bathroom circuit could be a general purpose circuit of 15 amps but the receptacle was required to be Ground Fault Circuit Interrupter protected. Even the kitchen circuits could be a 15 amp circuit but the kitchens were to be 20 amps in the 1990 cycle.

The requirement for the bathroom receptacle to be on a 20 amp circuit came about in the 1996 cycle.

I hope this helps and welcome to the forum.
 