Not sure. Page 34 for water piping shows it on the supply. They usually are last though. I was thinking there might be a check built into the circulator that is messing things up. Does your gauge record pressure spikes with a tattle tail needle? In your picture the condensate is in that same area also. It'd be nice to make sure that it's water expansion causing the relief to trip and not something else.

Page 34 is domestic hot water. The pressure gauge in the boiler reads a few pounds higher than the external gauge. Neither seems to fluctuate much.


Your pressure is running 21 lbs? Why its floor heat? What air pressure is in the expansion tank cold system 100* f or less? How many gallons of water in the system and model and brand of ex tank? 30* td across boiler would like to see more flow 20* but its ok.

It's this tank.
https://www.supplyhouse.com/Amtrol-102-1-30-Extrol-EX-30-Expansion-Tank-4-4-Gallon-Volume
It was charged to 15psi when I installed it. The system has about 16 gallons of water.
 

John Gayewski

In the Trades
Messages
4,368
Reaction score
1,350
Points
113
Location
Iowa
I just stumbled across this.
https://www.supplyhouse.com/Weil-McLain-383-100-060-AquaBalance-Easy-Up-Manifold-Kit-for-Combi-80-120-155-Boilers?utm_source=Facebook&utm_medium=catalog sales&utm_campaign=cross-upsell&utm_content=ntm&fbclid=IwAR1kMdUa987sDs1MtC_DgnsXW4zPNXais6Llu43NM8I7xPgZ-h0XjLlb1ls
That seems to indicate by relief valve is in the right spot. which then leads to believe the check valve is my issue. Or maybe I just put too much water in the system.
There's no such thing as too much water in the system it needs to be completely full. Your expansion tank only needs to have less than .5 gal. In capacity.
 
Last edited:

John Gayewski

In the Trades
Messages
4,368
Reaction score
1,350
Points
113
Location
Iowa
I just stumbled across this.
https://www.supplyhouse.com/Weil-McLain-383-100-060-AquaBalance-Easy-Up-Manifold-Kit-for-Combi-80-120-155-Boilers?utm_source=Facebook&utm_medium=catalog sales&utm_campaign=cross-upsell&utm_content=ntm&fbclid=IwAR1kMdUa987sDs1MtC_DgnsXW4zPNXais6Llu43NM8I7xPgZ-h0XjLlb1ls
That seems to indicate by relief valve is in the right spot. which then leads to believe the check valve is my issue. Or maybe I just put too much water in the system.
The check valve should not be at the inlet of the pump. Check valves get fouled and can ruin your pump. I don't think it's a great idea to contradict the manufacturer's diagram, but the check should not be at the inlet like that.

I personally would move it. Maybe temporarily get rid of it and see how it performs.
 

John Gayewski

In the Trades
Messages
4,368
Reaction score
1,350
Points
113
Location
Iowa
How would I detect that?

Wouldn't that mean the check valve should be on the supply/output side of the primary loop?
It stops the water really no matter where it's at, but I do think it should be over there, as I've been saying. It's just tough for me to contradict what the manufacturer has.
 

Reicherb

Member
Messages
189
Reaction score
2
Points
18
Location
Linden, MI
I took out the check valve and the pressure relief is no longer leaking. Everything seems to be working well. Should I leave it as is or install a check valve on the supply side?
 

John Gayewski

In the Trades
Messages
4,368
Reaction score
1,350
Points
113
Location
Iowa
I took out the check valve and the pressure relief is no longer leaking. Everything seems to be working well. Should I leave it as is or install a check valve on the supply side?
If your happy leave it. If you start to notice flow where there shouldn't be put it on the supply side.
 

Fitter30

Well-Known Member
Messages
4,383
Reaction score
803
Points
113
Location
Peace valley missouri
For some reason the built in pump and the spring check had to built pressure between them of off cycle over pressuring the relief.
 

Fitter30

Well-Known Member
Messages
4,383
Reaction score
803
Points
113
Location
Peace valley missouri
For some reason the built in pump and the spring check had to built pressure between them of off cycle over pressuring the relief. Put a swing check on the supply side on a horizontal line just on the secondary loop discharge side of pump if it doesn't have a built in check. Install manual doesn't want one on the primary.
 

Fitter30

Well-Known Member
Messages
4,383
Reaction score
803
Points
113
Location
Peace valley missouri
Check on primary loop
 

Attachments

  • Screenshot_2021-12-05-21-49-38.png
    Screenshot_2021-12-05-21-49-38.png
    190.9 KB · Views: 147
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks