Not sure. Page 34 for water piping shows it on the supply. They usually are last though. I was thinking there might be a check built into the circulator that is messing things up. Does your gauge record pressure spikes with a tattle tail needle? In your picture the condensate is in that same area also. It'd be nice to make sure that it's water expansion causing the relief to trip and not something else.
Page 34 is domestic hot water. The pressure gauge in the boiler reads a few pounds higher than the external gauge. Neither seems to fluctuate much.
Your pressure is running 21 lbs? Why its floor heat? What air pressure is in the expansion tank cold system 100* f or less? How many gallons of water in the system and model and brand of ex tank? 30* td across boiler would like to see more flow 20* but its ok.
It's this tank.
https://www.supplyhouse.com/Amtrol-102-1-30-Extrol-EX-30-Expansion-Tank-4-4-Gallon-Volume
It was charged to 15psi when I installed it. The system has about 16 gallons of water.