Triangle Tube Prestige Solo 175 Boiler, Constant CH call? Help

Users who are viewing this thread

steve9273

New Member
Messages
1
Reaction score
0
Points
1
Location
Connecticut
I have a Triangle Tube Prestige Solo 175 Boiler. Runs on propane and is about 9 years old.

Lately I have noticed that the Boiler had been turning on quite frequently, even when the thermostats are all off and no hot water is being used. It will run for a few minutes, reach is setpoint, turn off for a few minutes, and repeat the cycle.

After downloading the manual I realized that there was a continous CH1 and CH2 call, even though the thermostats are all off. I verified that there was a CH call by navigating to the information menu on the Boiler.

How can I troubleshoot where the issue is?

Additional information:
1) The home has 5 zones and Thermostats
2) It controls radient heat (primary), as well as forced hot air. Domestic hot water (however that seems fine)
3) It is connected to a Buderus LT200 - 53 Gal. - Horizontal Indirect Water Heater.

I even disconnected the thermostat wires to the Boiler, yet it still has a CH1 and CH2 call (as a test).
 

Fitter30

Well-Known Member
Messages
4,758
Reaction score
917
Points
113
Location
Peace valley missouri
7-8 terminals are heating
11-12 terminals are dhw
If you read 24 vac between them not calling for heat
0 vac calling for heat
 