I need to run water to a bathroom addition I'm building. I'm using a 3/4" PEX run with 1/2" branching off to fixtures. I need to tie into the water pipes and would like to do that at the water heater so as to bypass the rest of the house plumbing which has 1/2" hot water pipe. I'm not replacing the gas water heater at this time as it is still working fine.

All pipe from the service entry to the water heater is in 3/4" copper. I plan to replace the water heater supply lines (they are old and nasty looking) and solder in some 3/4" tees at the same time and transition to my 3/4" PEX lines which will then make the 50 foot journey to the new bathroom. Please see the attached diagram which shows how I plan to connect the PEX to the system near the water heater.

Is this OK, or should I plan to do something else. I'm set on PEX, but not violating code is important, especially since this will all be inspected. I live in Phoenix, AZ. Thank you.

WH Setup.jpg
 
Last edited by a moderator:

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
Plastic piping should not be attached to a water heater. You want at least 18" of copper off the top the heater and then transition to PEX.

UPC Code 604.11.2 Water Heater Connections. PEX tubing shall not be installed within the first eigthteen (18) inches (457 mm) of piping connected to a water heater
 
Last edited by a moderator:

Jeepnick

New Member
Messages
18
Reaction score
0
Points
0
Location
Phoenix, AZ
I suppose my diagram isn't that clear. The PEX transition will be near the ceiling which means there will be roughly 3 feet of copper between the pex and the water heater.

Any other considerations? Thank you.
 
Last edited by a moderator:

Hackney plumbing

Homeowner
Messages
1,130
Reaction score
3
Points
38
Location
Alabama
Plastic piping should not be attached to a water heater. You want at least 18" of copper off the top the heater and then transition to PEX.

Is that true with electric water heaters also or is the 18" rule just for gas? If it applies to electric whats the reasoning behind it other than it's code? How far should a pex connection be away from the vent pipe of the water heater? You can install 18" of copper to the water heater but if thats vertical rise and the vent pipe is vertical rise they would still be close to each other......
 

renstyle

New Member
Messages
13
Reaction score
0
Points
0
Location
Boone, Iowa
From another layman's POV, it seems fine. 3/4" PEX should handle the 50' distance without much issue. The only real *concern* I would have had was also the WH-PEX clearance, which at 3' you've accounted for (and then some).

I too have heard that while CVPC is not to be run directly to the hot side of a WH (and the cold if WH is gas), PEX can potentially run straight off the WH. Even if it was perfectly safe, I would never chance it if I didn't have to. I've accidentally touched my flue while the WH was running... WAY out of my personal comfort zone when using PEX.

What you did with keeping the 3' lines is exactly what I would have done in your shoes.
 

hj

Master Plumber
Messages
33,608
Reaction score
1,047
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
The hottest water in the tank is at the top, and it applies to both hot and cold pipes. That heat will rise in the connecting pipes, but lose temperature to the air, which is why they want BOTH lines to have copper for 18" from the tank.

UPC Code 604.11.2 Water Heater Connections. PEX tubing shall not be installed within the first eigthteen (18) inches (457 mm) of piping connected to a water heater
 
Last edited by a moderator:

Hackney plumbing

Homeowner
Messages
1,130
Reaction score
3
Points
38
Location
Alabama
The hottest water in the tank is at the top, and it applies to both hot and cold pipes. That heat will rise in the connecting pipes, but lose temperature to the air, which is why they want BOTH lines to have copper for 18" from the tank.

Do what? So your saying the plumbing code wants 18" of copper because of heat loss??? You dont think copper losses heat? LOL
 

Hackney plumbing

Homeowner
Messages
1,130
Reaction score
3
Points
38
Location
Alabama
Come on guys.....They want copper the first 18"of a gas water heater because that part of the vent gets the hottest,especially when the vent is cold and the heater fires...... After that you must still stay at least 6" away from the vent pipe.

At least one pex manufacturer doesn't give two craps if you install pex directly to an electric water heater. Some codes do not allow it because their ignorant and the code is not perfect and thats one of a few reasons why its always changing.
 
Last edited:

MACPLUMB

In the Trades
Messages
1,080
Reaction score
83
Points
48
Location
HOUSTON, TEXAS
Wrong hackney sorry to say i found this out the hard way !

The 18" is to keep the plastic from melting from the hot water backing into the pipes this goes for gas or
electric both by the time hot water rises 18" from the heater heat loss is enough to cool the water to below
the melting point of plastic piping ie, cpvc, pex, sch. 40 piping etc.
 

MACPLUMB

In the Trades
Messages
1,080
Reaction score
83
Points
48
Location
HOUSTON, TEXAS
Wrong Hackney sorry to say I found this out the hard way !

The 18" is to keep the plastic from melting from the hot water backing into the pipes this goes for gas or
electric both by the time hot water rises 18" from the heater heat loss is enough to cool the water to below
the melting point of plastic piping ie, cpvc, pex, sch. 40 piping etc.

THIS IS WHY IT IN THE U.P.C. CODE BOOK

UPC Code 604.11.2 Water Heater Connections. PEX tubing shall not be installed within the first eigthteen (18) inches (457 mm) of piping connected to a water heater
 
Last edited by a moderator:

Hackney plumbing

Homeowner
Messages
1,130
Reaction score
3
Points
38
Location
Alabama
Wrong Hackney sorry to say I found this out the hard way !

The 18" is to keep the plastic from melting from the hot water backing into the pipes this goes for gas or
electric both by the time hot water rises 18" from the heater heat loss is enough to cool the water to below
the melting point of plastic piping ie, cpvc, pex, sch. 40 piping etc.

THIS IS WHY IT IN THE U.P.C. CODE BOOK

You got so excited you posted it twice!!!

I dont care what code book it's in thats non-sense. Post your source or a link.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
I dont care what code book it's in thats non-sense. Post your source or a link.

You seem to want to do things your way, regardless of the code. If you really think it's bunk, petition to have it changed. In the meantime, it behooves you to abide by the codes. When you got your license, you agreed to do this whether you thought it was good or not. You can always do it more robustly, as long as it is still code (code is the minimum standard), but that's between you and your customer and the building inspector, whether you have to satisfy one or not.
 

Hackney plumbing

Homeowner
Messages
1,130
Reaction score
3
Points
38
Location
Alabama
You seem to want to do things your way, regardless of the code. If you really think it's bunk, petition to have it changed. In the meantime, it behooves you to abide by the codes. When you got your license, you agreed to do this whether you thought it was good or not. You can always do it more robustly, as long as it is still code (code is the minimum standard), but that's between you and your customer and the building inspector, whether you have to satisfy one or not.


I dont think you understand. No code book says that the hot water coming from a water heater will melt pex and if you keep it 18" away it will not melt. Thats CRAP. and its not in a code book. If it is....some guy in his moms basement wrote the book and named it code book.

Google Zurn Pex installation guide and download the PDF. And read it.

People can have their own opinion but they cant have their own set of facts

Do I know more than most of the code book writers about plumbing? I KNOW I DO...I school inspectors and "plumbing authorities" on the regular.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
That close to a flue of a gas WH CAN damage pex or cpvc. Probably fine with an elecric WH, but I didn't think the codes differentiated type.
 

Hackney plumbing

Homeowner
Messages
1,130
Reaction score
3
Points
38
Location
Alabama
That close to a flue of a gas WH CAN damage pex or cpvc. Probably fine with an elecric WH, but I didn't think the codes differentiated type.

. Codes may not allow it but that doesn't mean its wrong in practice. WTH in chicago they cant use pvc....what a freakin joke. Code will not allow it.

Zurn expressly says that connecting pex to an electric water heater is perfectly acceptable.
 

hj

Master Plumber
Messages
33,608
Reaction score
1,047
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; So your saying the plumbing code wants 18" of copper because of heat loss???

Do you have a problem with comprehension? The copper is to protect the plastic from the hottest water at the top of the tank, NOT to "Cool" down the tank.

UPC Code 604.11.2 Water Heater Connections. PEX tubing shall not be installed within the first eigthteen (18) inches (457 mm) of piping connected to a water heater
 
Last edited by a moderator:

Hackney plumbing

Homeowner
Messages
1,130
Reaction score
3
Points
38
Location
Alabama
quote; So your saying the plumbing code wants 18" of copper because of heat loss???

Do you have a problem with comprehension? The copper is to protect the plastic from the hottest water at the top of the tank, NOT to "Cool" down the tank.

I dont think you comprehend that the tube is rated for continuous hot water use. How does the water cool off with a hot water recirculating system? Riddle me that? Do you really think 18" of copper is going to make any substantial difference in temp with the hot water circulating through the system?

Goodluck explaining that one and making any sense.

Infact Nibco only requires the tube be 12" away from a gas water heater........

ZURN requires separation only for GAS water heaters. Zurn says its fine to connect their pex directly to electric water heaters. IS it your position that gas water heaters heat water hotter than electric? Please explain so I can comprehend that....

NIBCO® PEX Fixture Connections
• A metal adapter at least 12” long should be used to connect NIBCO® PEX tubing to a gas water heater. The tubing
must be at least 6” from the exhaust vent.
• NIBCO® PEX tubing can be connected directly to an electric water heater using metal insert adapters.
• NIBCO® PEX tubing can be connected to PEX insert accessories as long as the barb meets ASTM F 1807 specifications.
Such accessories include supply stop valves, ball valves, icemaker boxes, washing machine boxes, copper stub-outs and manifolds,
 
Last edited:

Hackney plumbing

Homeowner
Messages
1,130
Reaction score
3
Points
38
Location
Alabama
Copied from Zurn.....I guess they dont comprehend well either......

Zurn PEX may be connected directly to
electric water heaters for residential
plumbing applications. Zurn PEX has brass
male and female threaded adapters and
swivel adapters that can be used for this
application.
Zurn PEX must be kept at least 6" away
from the exhaust vent of a gas-fired water
heater. This is easily accomplished by
using flexible water heater connectors.
When the inlet and outlet connections are
well away from the exhaust vent, such
as most heaters with side connections,
Zurn PEX may be connected directly to
the water heater.
 

Hackney plumbing

Homeowner
Messages
1,130
Reaction score
3
Points
38
Location
Alabama
More from Viega......

ViegaPEX Ultra tubing is
manufactured to ASTM F876/F877
standards and listed to ANSI/NSF
Standards 14 and 61. It is chlorine
resistance rated for both traditional
and continuous recirculation PEX
5006 (CL5) applications. ViegaPEX
Ultra tubing is rated at 100 psi at
180°F and 160 psi at 73°F.

Temperature and Pressure Ratings:
• 200°F at 80 psi
• 180°F at 100 psi
• 73.4°F at 160 psi

PureFlow tubing should not
be connected directly to gas-fired
water heaters. The high temperatures
of these appliances can damage
the tubing.
When connecting a PureFlow system
to a gas-fired water heater, install a
minimum of 18" of metallic piping
beween the water heater and tubing,
keeping tubing more than 6" away
from the vent pipe. Where local
code allows, PureFlow tubing may
be connected directly to electric
water heaters and used for hot water
recirculation lines which do not come
within 6" of the gas heater vent.

...................................................................................................................................................

I hope everyone comprehends this info. You can have your opinions but not your own facts.
 