Zone Valve Wiring - Abandoning red wires.

Discussion in 'Boiler Forum' started by philtrap, Apr 11, 2021.

  1. philtrap

    philtrap Member

    Joined:
    Jun 19, 2013
    Occupation:
    Civil Engineer
    Location:
    Long Island, NY
    Folks – I have a Honeywell zone valve (v8043e1012). As you know it has 4 wires, 2 red 1 yellow and 1 orange. I want to move the connections from a taco sr501 to a taco 2vc404 to an open spot for other reasons… My question is can I abandon the two red wires since they are not needed with the 404?


    Thanks
     
  2. fitter30

    fitter30 Well-Known Member

    Joined:
    Feb 2, 2020
    Occupation:
    Retired service tech
    Location:
    Peace valley missouri
    Yes red wires are just a end switch
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. philtrap

    philtrap Member

    Joined:
    Jun 19, 2013
    Occupation:
    Civil Engineer
    Location:
    Long Island, NY
    I thought so. Thanks so much!!!!
     