I am looking at wiring a Honeywell EIM into a boiler system, which is using RA832A switch. I am not very familiar with the wiring for boilers and their corresponding wiring. So any help on how the TT terminals from the switch would be wired into the EIM?
 

Fitter30

Well-Known Member
Messages
4,347
Reaction score
795
Points
113
Location
Peace valley missouri
Emi when heating calls RH to W closes putting out 24v to common. Ra relay needs a dry contact across T-T to energize relay so there not going to work together without a relay. What is the full model # of emi and what is sequence of operation trying to do.
 