wwhitney
In the Trades
On the wet vent connection for the WC (called a 3x3x2 wye), there's no venting upside to having more pitch than 2% on the branch inlet / wet vent. But it's OK to have a little more pitch if that makes the install simpler somehow.
On the elevation sketch, the right side is cut off, and that's the important side. The rule is that the part of the drain that is carrying both lavs, and is a wet vent for the WC, needs to be 2". The dry vent for the lavs (and ultimately WC) can be 1-1/2", as can any wet vent portion that that is only carrying one lav.
Cheers, Wayne
On the elevation sketch, the right side is cut off, and that's the important side. The rule is that the part of the drain that is carrying both lavs, and is a wet vent for the WC, needs to be 2". The dry vent for the lavs (and ultimately WC) can be 1-1/2", as can any wet vent portion that that is only carrying one lav.
Cheers, Wayne