Wallhung boilers outside sensor

Users who are viewing this thread

Plumber69

In the Trades
Messages
2,380
Reaction score
214
Points
63
Location
Prince Rupert, British Columbia
I installed a setup up with 2 wall hung boilers a low loss header and a teckmar with outside sensors. It was 2 degrees out and my primary loop was 150 and secondary loop only reached 130. It's for an small apartment with cast radiators
 

John Gayewski

In the Trades
Messages
4,360
Reaction score
1,345
Points
113
Location
Iowa
I installed a setup up with 2 wall hung boilers a low loss header and a teckmar with outside sensors. It was 2 degrees out and my primary loop was 150 and secondary loop only reached 130. It's for an small apartment with cast radiators
Your secondary pump isn't pumping enough.

To be sure your saying you only got 130 to the first radiator?
 
Last edited:

Fitter30

Well-Known Member
Messages
4,367
Reaction score
800
Points
113
Location
Peace valley missouri
What model tekmar? Usually theres 4 settings -outside shutoff temp, low temp, high temp and ratio. If i don't know the building start at 0* low,165* high, ratio 1 to 1 , shut off 68*. So at 0* 165*water at 65* 100* water. What has 2* difference? Draw a diagram how system is piped? Radiators piped reverse return?
 