Relacing old boiler with 2 wallhungs

Users who are viewing this thread

Plumber69

In the Trades
Messages
2,380
Reaction score
214
Points
63
Location
Prince Rupert, British Columbia
Old boiler has 2 1/2" send and return. On my new setup 1" comes off boilers with tie into 1 1/2" to the low loss header (primary loop). Should I keep it 1 1/2 then up size to 2 1/2 on secondary loop. Or run 2 inch on secondary loop. Will it make a difference

20211014_143046.jpg
 

Fitter30

Well-Known Member
Messages
4,292
Reaction score
778
Points
113
Location
Peace valley missouri
Hydro separator don't know what pipe size it is but keep as much 2.5" within a few feet. Usually ex tank is piped on the secondary loop.
 