Vent size for toilet, shower, and vanity for IPC

Users who are viewing this thread

Mayo

New Member
Messages
8
Reaction score
0
Points
1
Location
Michigan
Hey everyone,

I have a bathroom group that consists of a toilet, shower, and vanity.

The drain for the vanity is 2 inches and serves as a wet vent for the shower and the toilet. This is all pretty standard, but the tricky part is when the wet vent converts to a dry vent, I'd like to down size to 1.5 inches. This is because I have a 2x4 wet wall and I can't bore 2.5 inch holes (due to building code) to fit a 2 inch dry vent.

According to UPC a toilet must vent off a 2 inch pipe. However, I'm in Michigan and it follows the 2015 Michigan plumbing code which is the 2015 IPC. In the IPC it shows that any pipe must vent off a minimum half of its size. So my 3 inch toilet pipe has to have a 1.5 inch vent. According to the chart a 1.5 inch vent from a 3 inch pipe can service 10 dfu, a toilet, vanity, and shower add up to 6.

Therefore, I'm concluding that after the wet vent portion, I can convert to a 1.5 inch vent.

Am I missing something here? I don't see any hidden clause that says otherwise.
 

John Gayewski

In the Trades
Messages
4,623
Reaction score
1,476
Points
113
Location
Iowa
I guess the wording in the section on wet venting would come into play here. Is there a portion of the wording that says "undiminished in size"? As in a wet vent shall be minimum 2" and blah blah blah... shall terminate undiminished in size blah blah blah...

@wwhitney would be the expert on these finer points in ipc.
 

wwhitney

In the Trades
Messages
6,846
Reaction score
1,938
Points
113
Location
Berkeley, CA
Under the IPC, a 1.5" dry vent at the lavatory suffices for wet venting a bathroom group. The portion of the wet vent carrying only 1 DFU (i.e. a single lavatory) can even be 1.5", but 2" is good.

Cheers, Wayne
 

Lukewalker64

New Member
Messages
14
Reaction score
1
Points
3
Location
Virginia, USA
Under IPC, when wet venting a bathroom group with a single vent at the lav, does it matter what order the drains join together? E.g., can the lav join a 3" pipe downstream of the water closet, then the shower and tub join the same pipe further downstream, before the 3" pipe flows into a vertical stack?

Does the answer change with more fixtures? E.g., a double lav and multiple shower heads?

If the sink is wet venting the entire bathroom group, does the vertical stack need to be vented?
 

Lukewalker64

New Member
Messages
14
Reaction score
1
Points
3
Location
Virginia, USA
Under IPC, when wet venting a bathroom group with a single vent at the lav, does it matter what order the drains join together? E.g., can the lav join a 3" pipe downstream of the water closet, then the shower and tub join the same pipe further downstream, before the 3" pipe flows into a vertical stack?

Does the answer change with more fixtures? E.g., a double lav and multiple shower heads?

If the sink is wet venting the entire bathroom group, does the vertical stack need to be vented?

Here's a rough drawing of what I'm considering, in case it's helpful. Would appreciate any feedback or thoughts.
bath plumbing.png
 