Tub and shower vent confusion

Users who are viewing this thread

Kenny Mapes

New Member
Messages
13
Reaction score
0
Points
1
Location
Florida
Tub and Shower branch I had this

shba1.PNG


But then thought the bathtub was not vented properly.
The location of the vent pipe is the only place this branch runs under a wall.

Should the BT arm come in downstream of the vent pipe to properly vent this?

Both trap arms are less than 6 feet.
 
Last edited:

Kenny Mapes

New Member
Messages
13
Reaction score
0
Points
1
Location
Florida
I thought this might be better
shba3.PNG

Would this require a clean out?
I quoted the wrong trap arm length for 2" it should be less than 5 feet.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,461
Points
113
Location
Bothell, Washington
Website
terrylove.com
The first one is better. Having the vent on the vertical of a line that is constantly washed is better than a horizontal line that may never be snaked or cleaned. It would be, but what are the odds?

wet_vent_upc_3_4_bath.jpg
 