Tricky Bathroom Drain Layout

Users who are viewing this thread

ScottyDee

New Member
Messages
9
Reaction score
0
Points
1
Location
Wisconsin
Hello everyone,

This is my first time posting and would like some help with a very tricky 2nd floor plumbing layout. I would like to take a week off of work and tackle this project. There are two bathrooms upstairs that are split between the toilets and showers. I have 9 and a half foot tall ceilings and will be doing a drop ceiling to make room for the drains. All of the cast iron has been removed and I sistered all the 2x10 joists (they were cut out with large holes where the 4 inch cast iron used to be)

The closest toilet is within 6 feet from the 4" stack so i'm assuming this will be okay
The closest shower is within 5 feet from the 4" stack

There is not much room to add vertical vents so i would like to do this with a horizontal layout if possible utilizing the main 4" vent and the 2" vent

Please feel free to make any additions, changes, or a new layout if this doesn't work

Attached is the layout I came up with after some brainstorming for a few days.
1) Will this layout work?
2) Is the 2 inch vent sufficient for this layout (this is the largest i can go)
3) does it matter which ties into the main 4" stack first (toilets vs showers)
4) Will there be any issues with the 2x2x2 wye that ties the showers & toilets to the vent (water draining from upstairs vanity)
5) Is the closest shower okay, or do i somehow need to get a vent in between the closest shower and the 4' stack)?
6) Would it make more sense to just branch off from the 4" horizontal run to the 2" showers than have a separate connection to the stack
 

Attachments

  • Floor Plan.jpg
    Floor Plan.jpg
    27.6 KB · Views: 155
  • Bathroom first floor.jpg
    Bathroom first floor.jpg
    22.2 KB · Views: 153
  • updated upstairs.jpg
    updated upstairs.jpg
    33.6 KB · Views: 152
Last edited:

ScottyDee

New Member
Messages
9
Reaction score
0
Points
1
Location
Wisconsin
Draw a floor plan.
Floor plan has been attached, I added vent locations. I also updated the original picture to include labeling and the second vanity

This will be a brand new layout, all of the original drains have been removed and PVC will be used. Let me know if you have any questions. Thanks!
 
Last edited:

James Henry

In the Trades
Messages
1,579
Reaction score
403
Points
83
Location
Billings, Montana.
If your planning on just using the far left lavatory as a wet vent, this should suffice. A single wet vent can accommodate 2 bathroom groups and the fixture to wet vent connection is considered the fixture to vent distance. CHECK YOUR CODE BEFORE YOU DO ANYTHING.
 

Attachments

  • Floor Plan.jpg
    Floor Plan.jpg
    32 KB · Views: 176

Mr tee

In the Trades
Messages
354
Reaction score
145
Points
43
Location
Montana
If the 4" stack is a vent for a fixture(s) on the first floor it is not legal to use it for a second floor drain.
 

ScottyDee

New Member
Messages
9
Reaction score
0
Points
1
Location
Wisconsin
If the 4" stack is a vent for a fixture(s) on the first floor it is not legal to use it for a second floor drain.
Would the use of air admittance valves on the first floor remedy this? I can add one to the shower drain and vanity drain. Would I need an additional AAV for the toilet? It’s located a couple feet from the main stack with a 4 inch wye. Thanks! I will add a floor plan and sketch of the layout Of the first floor on my lunch break

I attached the first floor plan with aavs to the original post. Will these AAV's work?
 
Last edited:

ScottyDee

New Member
Messages
9
Reaction score
0
Points
1
Location
Wisconsin
If your planning on just using the far left lavatory as a wet vent, this should suffice. A single wet vent can accommodate 2 bathroom groups and the fixture to wet vent connection is considered the fixture to vent distance. CHECK YOUR CODE BEFORE YOU DO ANYTHING.

Thank you very much. This really simplifies things for me
 

Mr tee

In the Trades
Messages
354
Reaction score
145
Points
43
Location
Montana
The approval of AAVs depends on where you are. However, they only protect traps from negative air pressure and the danger in your situation is possible positive pressure so they would be ineffective.
 

ScottyDee

New Member
Messages
9
Reaction score
0
Points
1
Location
Wisconsin
After the first shower you must transition to 3" drain then after the second toilet you could go to 4" depends on your code.

James after looking more closely at your picture and description i think this is the layout you are describing. Let me know if i'm wrong. Thanks!
 

Attachments

  • updated upstairs.jpg
    updated upstairs.jpg
    33.6 KB · Views: 154

James Henry

In the Trades
Messages
1,579
Reaction score
403
Points
83
Location
Billings, Montana.
There are problems with the first floor plumbing, are you able to reroute the drains and vents? If not the second story plumbing won't fly.
 

Attachments

  • updated upstairs.jpg
    updated upstairs.jpg
    35.4 KB · Views: 142

ScottyDee

New Member
Messages
9
Reaction score
0
Points
1
Location
Wisconsin
There are problems with the first floor plumbing, are you able to reroute the drains and vents? If not the second story plumbing won't fly.
The approval of AAVs depends on where you are. However, they only protect traps from negative air pressure and the danger in your situation is possible positive pressure so they would be ineffective.

I am able to run a vent pipe vertically, parallel to the main 4 inch stack and can tie it back in above all the second floor fixtures. Will something like this work?
 

Attachments

  • venting.jpg
    venting.jpg
    21.1 KB · Views: 138

ScottyDee

New Member
Messages
9
Reaction score
0
Points
1
Location
Wisconsin
This would be the best solution but I don't know what I have to work with.

the upstairs would be vented with both the 4 inch pipe that goes through the roof on the right side of the picture and the 2 inch vent that goes through the roof on the left side of the picture. Will the 2 inch vent that goes through the roof eliminate the need to run additional venting for the first floor?
 