Steven Tyminski
Hi,
I'm Steve from southeast AZ, near Tombstone.
I have a situation where my overload breaker on my well pump control box clicks a few times then trips (opens).
I tested the run and start capacitors and found them good.
I tested resistance of my 2HP/25GPM Grundfos pump, installed in 1994 at 300', and found, using the formula for pump motor resistance of wire colors B+R = (Y & R) + (Y + B)
Test shows B&R = 9.6 ohms / (Y & R) + (Y + B) = 3.2 + 7.3 = 10.5. ohms
Difference of .9 ohms, test tolerance limits being unknown, this reading may be within spec.
I tested the current draw of the pump and found wire colors R=8 amps / Y=20 amps / B=22 amps, starting then running R=0.
When the overload breaker is making the clicking sound before it trips, current on the black wire fluctuates between 22 and 25 amps.
I tested resistance to ground on the 20K scale and found 10K ohms on each wire to ground with my DVM constantly fluctuating. never reaching zero or infinity.
My analog VOM doesn't work above the 10K range. I don't have a megger.
Local guy, who seems knowledgeable, says he thinks my pump run windings are beginning to fail. Wants to install a new similar pump for $1750 +labor. He says he finds the life expectancy of this pump is 8-12 years.
To me it seems like a bad underwater splice (based on resistance to ground test), a mechanical failure within the pump, or a combination both.
What do you guys think?
Thanks,
Steve
Thanks,
Steve