Fitter30
Well-Known Member
No the honeywell control
The wires from C1 and C2 go directly to the pump. Nothing in between. There are no other part numbers other than L8148E.Where do the pumps wire go to? Take a pic if that honeywell control find the model number.
W to T what voltage should be 24. Yes 24VTop terminals with thermostat calling for heat
W to T what voltage should be 24
W to TV what voltage should be 24
Two terminals left of relay, red and blue wires could be 120 what voltage? Kill power. If theres voltage jump terminals together. Power boiler back up
And what are your thoughts on a like for like replacement? Supplyhouse has either the L8148E1265 or L8148E1299. I can't tell the differance between them.
That honeywell has a high limit control that's the red and blue wires. So to replace it need a transformer, relay and a limit control or boiler control. Need to remove old control to see what size bulb it has or replace the well to fif a new sensor.
Just want to make sure I am reading this correctly. You are suggesting the 1265 as the replacement assuming the bulb size is the same. Is that correct?1265 the 1299 can be on mv systems. Be shure to check bulb size on the old control to see if the well has to be changed.
What does that mean?The well is discontinue from what i read.
If the bulb doesn't fitter in your well they don't make the replacement well that fits the new bulb. Going to check to check with honeywell..What does that mean?