About to install kitchen sink using an AAV, I have a leftover tee fitting, wondering if I can use that flat or need a wye and turn or whatever it is called, also is there a minimum height for the AAV to be above the horizontal drain, thanks again
 

Tuttles Revenge

In the Trades
Messages
4,459
Reaction score
1,575
Points
113
I would use a tee on its back under a sink.. Its only allowing air in.. because it prevents liquid from entering that vertical section, I can't see it needing to be a drainage fitting. In the UPC code, the pipe after the AAV needs to be 2" ... I always install my AAV in the wall in a recessed box made for the purpose. The AAV needs to be a minimum of 4" above the trap arm.
 

Reach4

Well-Known Member
Messages
41,398
Reaction score
4,994
Points
113
Location
IL
VT appears to use IPC.

However 2 inch drain pipe for a kitchen appears wise. The common place for a clog beneath a kitchen sink is where the drain transitions from vertical to horizontal. Having a way to snake that area is good.
 