Bannerman
Well-Known Member
Your pump currently delivers water at 15 gpm or as you now calculate, 13.98 gpm whenever it is running. If you are operating only 1 sprinkler consuming 4.1 gpm, once the system pressure drops to 40 psi, the pump will again pump 13.98 gpm so (13.98 - 4.1) 9.88 gpm will refill the pressure tank until the pump shuts off at 60 psi. The high-low-high pressure cycle will continue to repeat for as long as that sprinkler continues to flow water. The pressure to the sprinkler (or a shower, laundry, DW etc) will continually fluctuate between 40-60 psi.
A CSV will control the delivery from the pump, to satisfy the gpm that is actually being used once the pump is running. With a 40/60 pressure switch, the system pressure will drop as usual to 40 psi to start the pump, but once started, the system pressure will rapidly rise to 50 psi where it will remain consistent @50 psi as long as between 1 gpm - <13.98 is flowing. Once water use is stopped, the CSV will then allow only 1 gpm from the pump to finish filling the pressure tank to 60 psi to cause the pressure switch to shut off the pump.
A pressure tank size is typically determined by calculating the pump's delivery rate, to allow the pump to run for at least 60 seconds minimum once started. Because a CSV will limit the pump's flow rate to 1 gpm when flowing only to the pressure tank, a large tank will not be needed to provide the minimum pump run time.
Because the system pressure will need to drop from 60-40 psi before the pump will start, a large tank will result in longer flow time before the pressure will fall to 40 to start the pump to provide 50 psi consistently. A smaller pressure tank's pressure will fall more rapidly, thereby allowing the pump to run sooner and will thereby deliver a consistent 50 psi quicker than when a larger pressure tank is used.
A CSV will control the delivery from the pump, to satisfy the gpm that is actually being used once the pump is running. With a 40/60 pressure switch, the system pressure will drop as usual to 40 psi to start the pump, but once started, the system pressure will rapidly rise to 50 psi where it will remain consistent @50 psi as long as between 1 gpm - <13.98 is flowing. Once water use is stopped, the CSV will then allow only 1 gpm from the pump to finish filling the pressure tank to 60 psi to cause the pressure switch to shut off the pump.
A pressure tank size is typically determined by calculating the pump's delivery rate, to allow the pump to run for at least 60 seconds minimum once started. Because a CSV will limit the pump's flow rate to 1 gpm when flowing only to the pressure tank, a large tank will not be needed to provide the minimum pump run time.
Because the system pressure will need to drop from 60-40 psi before the pump will start, a large tank will result in longer flow time before the pressure will fall to 40 to start the pump to provide 50 psi consistently. A smaller pressure tank's pressure will fall more rapidly, thereby allowing the pump to run sooner and will thereby deliver a consistent 50 psi quicker than when a larger pressure tank is used.