Bull. You are messing up. You should get a pressure gauge, as Brian did, and if you have a check valve feeding your personal unit, find that you most likely don't meet your own criterion.Your goal should be to keep the worst case pressure below 80psi, regardless of how much of the WH capacity you should use. Size your tank accordingly.
Are you backing away from claiming that the thermal expansion tank should keep the expanded water pressure to 80 or less, or are you moving to something else?To minimize the wear and tear on hoses, seals, valves, cartridges, and to help prevent blasting a glass out of your hand when filling it after the ET is filled to max, size it so that your max pressure doesn't exceed the plumbing code's value. Yes, the WH is tested to 300psi, and the T&P valve should open at 150, but having your pressure high, for what could be most of the day after everyone showers and then leaves home for work and/or school, is not ideal. The goal of using a PRV is to limit the max pressure to a code maximum value...a larger ET is relatively cheap, and by minimizing the amount of flex it has to do, will also extend its life, saving money in the long term.
FWIW, the OP's ET was determined to be defective, and he's replacing it...this should minimize the peak pressures seen.
No, ideally, you'd keep the pressure below the code maximum under all conditions. The fact that systems can exceed that does not change the fact that code wants it less than 80, or the fact that seals, valves, hoses, etc. do not like more than that. As I said, worst case, with everyone showering, then going off to school or work...the excessive pressure could be sitting in the system for many hours...that is not ideal..Are you backing away from claiming that the thermal expansion tank should keep the expanded water pressure to 80 or less, or are you moving to something else?
If you were to make your own spreadsheet, using Boyles law, one of the factors would have to be the max pressure to design to. If you presume non-expanded water pressure was 70, and precharge was 70, with a 50 gallon wh, you would compute the need a much larger pressure tank than the recommendation tables ever call for.No, ideally, you'd keep the pressure below the code maximum under all conditions. The fact that systems can exceed that does not change the fact that code wants it less than 80, or the fact that seals, valves, hoses, etc. do not like more than that. As I said, worst case, with everyone showering, then going off to school or work...the excessive pressure could be sitting in the system for many hours...that is not ideal..