Needing expansion tank after changing waterheater?

Discussion in 'Water Heater Forum, Tanks' started by bigbird454, Feb 14, 2019.

  1. bigbird454

    bigbird454 New Member

    Joined:
    Jul 26, 2018
    Location:
    Massachusetts
    Long story short. Recently had old water heater, 40 gallon Bradford White, replaced by a new plumber with an American Standard. (New plumber was at the house working on a remodel so we used him instead of calling our tried and true plumbing co.) Now we have water coming out of the pressure relief valve whenever we use a lot of hot water (washing 3 loads of clothes). New plumber either does not care or does not seem to believe this. After educating myself, looking at the American Standard owners manual, I believe we need an expansion tank. We are on a closed system, with a pressure relief valve on cold water line. We have also lowered the thermostat on the water heater, lowest position. Why didn't we have this problem with the Bradford White water heater? Is there something special about them? Do they have special features other water heaters don't have? Many thanks.
     
  2. Reach4

    Reach4 Well-Known Member

    Joined:
    Sep 25, 2013
    Location:
    IL
    You possibly need a larger expansion tank. The new HW tank may be larger, or may be set hotter.

    You may have used more HW having built up a backlog of laundry and showers. The old one may have only had half of its hot water replaced with cold each time, but the new one had almost all of its water replaced with cold, as you worked down the backlog.

    The precharge would ideally be set to the maximum water pressure the city supplies (4 am typically). But setting it a couple psi higher than the daytime water pressure is good. The air precharge should be set with the water pressure near zero. Of course getting a new WH did not change the water pressure from the city.

    It is also possible that the existing expansion tank happened to fail -- just coincidence.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. phog

    phog Active Member

    Joined:
    Jul 29, 2017
    Location:
    Rochester NY
    A dripping faucet, running toilet etc can also serve to relieve the pressure from hot water expansion, if you had any existing fixtures updated & the old leaks are now gone, that could be why.
     
  5. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    If you pick up a pressure gauge you can check the static water pressure in the home.
    PSI over 80 gets a pressure reducing valve. They can fail over time.

    [​IMG]
     
  6. WorthFlorida

    WorthFlorida The wife is still training me.

    Joined:
    Oct 28, 2009
    Occupation:
    Retired
    Location:
    Orlando, Florida
    The old water heater the pressure relief valve could have had corrosion at the valve and prevented it from opening.
    As said before the cause of your current problem is the cold water is expanding enough that the pressure is getting somewhere around 150 psi or close to it. As Terry suggest, get the pressure gauge with a tattletale needle. The pressure needle will push the red needle to the highest pressure and it will stay there until you manual move it back to zero. This is so you don’t have to babysit it.
     
Similar Threads: Needing expansion
Forum Title Date
Water Heater Forum, Tanks ? Home water pressure and needing Pressure Regulatory valve Feb 4, 2013
Water Heater Forum, Tanks Whirpool 50g gas heater thermal expansion problems Jul 27, 2020
Water Heater Forum, Tanks Dark Rust on Water Intake Connection to Expansion Tank May 23, 2020
Water Heater Forum, Tanks Where to begin with expansion tank Apr 29, 2020
Water Heater Forum, Tanks Where to install thermal expansion tank Mar 22, 2020

Share This Page