Need some advice on baseboard BTU and length

Users who are viewing this thread

MrMackster

New Member
Messages
8
Reaction score
0
Points
1
Location
Massachusetts
My plumber is coming in two weeks and I wanted to be able to have an intelligent conversation about this.

I remodeled my second floor, all new insulation, windows, and R60 in my attic. The previous owners converted from steam radiators to hot water baseboard 20+ years ago and I am pretty sure they put down way too many feet of baseboard and now with the remodel its even worse. I need to replace the baseboard in two rooms due to damage. The rooms are small, 12x10 and 11x10 with two windows each. They have 2 six foot sections of fins! Everything is in series and there are the last two rooms in a 5 room loop (all about 2700-3000 BTU required)

I used coolcalc and slant fin's tool to figure out BTU requirements and they both came up with about ~2700 BTU per room which is only about 5-6 feet total of baseboard. Should I downside from 2 six footers to 2 three footers? Anything I should be concerned about? Right now I run at 180 degrees, but I would like to lower it at some point to get it to condense better, but I am sure if that means I should be putting the same amount or less of baseboard. Any advice would be appreciated, my plumber is more of a water/waste plumber and less a heat plumber.
 

Fitter30

Well-Known Member
Messages
4,338
Reaction score
791
Points
113
Location
Peace valley missouri
If your just wanting to lower the capacity the fins can be covered and that will stop the air flow rising . Another way is a boiler reset control that will vary boiler temperature by outdoor temperature
 

MrMackster

New Member
Messages
8
Reaction score
0
Points
1
Location
Massachusetts
If your just wanting to lower the capacity the fins can be covered and that will stop the air flow rising . Another way is a boiler reset control that will vary boiler temperature by outdoor temperature

Yeah, was just reading that. Maybe a good idea to just replace what's there now and cover the fins later if needed. And yes, my boiler has an outdoor reset functionality, but I am skeptical it will work correctly in my configuration.
 

Fitter30

Well-Known Member
Messages
4,338
Reaction score
791
Points
113
Location
Peace valley missouri
Minimum water temp on a cast iron boiler is 140* return. Baseboard really don't start to heat till 120*. Reset will save energy if you need 180* at 0* you won't need 180* at 65*. Easy set point 180* at 0* 140* at 65* 1* change outside temp .6* water temp.
 

MrMackster

New Member
Messages
8
Reaction score
0
Points
1
Location
Massachusetts
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks