Hello Everyone! First time posting.
I would like to install a DIY mini-split in my house and am looking for some input on equipment selection.
So far it appears that the MrCool DIY line of equipment is the most user-friendly package. I want to use a two-zone system with the ceiling cassettes in the main living level of my home
Air conditioning is the primary reason for doing the installation, but the heat will also be used. The math shows me that at current electric rates, it is even more economical than my woodstove, provided I’m not cutting my own wood!
Up until now, I have been cooling my house in the summer with 1 or 2 5000 BTU window units and one 5000 BTU portable A/C. They are sufficient and keep the temps and humidity down, but I’m sick and tired of the noise. I used to get away with just two 5000 BTU units, but summers are a bit warmer now and I believe the blown in insulation in my attic has compressed and I’m getting more heat through the ceiling.
My house is ranch style, so I was thinking that I’d put one cassette in the main living area which is open concept, and one cassette down at the bedroom end. At first I thought that the 27,000 BTU 2 zone system with a 9,000 and 18,000 ceiling cassette should do the job. The18,000 cassette would be for the main area, 9000 for the back bedroom area. However, after looking at the Heat Calc output it seems that I should use a smaller unit. The way my house was built, I don’t think the “Rule of Thumb” calculations are going to work. So maybe a smaller unit is appropriate.
Location is in Southern New Hampshire
Other than watching several install videos, I don’t have much more than that to start.
I did a heat load calc on my house when I built it 17 years ago and managed to find a copy. I have included the report. For this installation the basement is not included, only the upstairs. So I would reduce the total by that amount, correct?
My math shows these numbers for the upstairs:
Total Heat Gain 19,225 – Basement Heat Gain 8,367 = Upstairs Heat Gain 10,858 BTUH
Total Heat Loss 30,376 – Basement Heat Loss 12,912 = Upstairs Heat Loss 17,464 BTUH
What do you all think about the sizing?
Comments, questions or advice?
Thanks
I would like to install a DIY mini-split in my house and am looking for some input on equipment selection.
So far it appears that the MrCool DIY line of equipment is the most user-friendly package. I want to use a two-zone system with the ceiling cassettes in the main living level of my home
Air conditioning is the primary reason for doing the installation, but the heat will also be used. The math shows me that at current electric rates, it is even more economical than my woodstove, provided I’m not cutting my own wood!
Up until now, I have been cooling my house in the summer with 1 or 2 5000 BTU window units and one 5000 BTU portable A/C. They are sufficient and keep the temps and humidity down, but I’m sick and tired of the noise. I used to get away with just two 5000 BTU units, but summers are a bit warmer now and I believe the blown in insulation in my attic has compressed and I’m getting more heat through the ceiling.
My house is ranch style, so I was thinking that I’d put one cassette in the main living area which is open concept, and one cassette down at the bedroom end. At first I thought that the 27,000 BTU 2 zone system with a 9,000 and 18,000 ceiling cassette should do the job. The18,000 cassette would be for the main area, 9000 for the back bedroom area. However, after looking at the Heat Calc output it seems that I should use a smaller unit. The way my house was built, I don’t think the “Rule of Thumb” calculations are going to work. So maybe a smaller unit is appropriate.
Location is in Southern New Hampshire
Other than watching several install videos, I don’t have much more than that to start.
I did a heat load calc on my house when I built it 17 years ago and managed to find a copy. I have included the report. For this installation the basement is not included, only the upstairs. So I would reduce the total by that amount, correct?
My math shows these numbers for the upstairs:
Total Heat Gain 19,225 – Basement Heat Gain 8,367 = Upstairs Heat Gain 10,858 BTUH
Total Heat Loss 30,376 – Basement Heat Loss 12,912 = Upstairs Heat Loss 17,464 BTUH
What do you all think about the sizing?
Comments, questions or advice?
Thanks