Natural Gas Regulators in Series

Users who are viewing this thread

edwardkm68

New Member
Messages
1
Reaction score
0
Points
1
Location
Seattle, WA
I have a project where there is a 5"-14" w.c. regulator installed on the natural gas header line that leads to two separate condensing boilers. The natural gas lines on the boilers themselves also have regulators installed on them that are 5-15" w.c. This seems to be causing the boilers to fail on a low gas pressure alarm when put into high fire. Having two of essentially the same regulators in series like that doesn't seem like something that should be done, but I don't really know the exact effect it has and was hoping someone more well versed in this topic would be able to provide some insight as to what is happening. Regulators are a fairly new topic for me and searching online hasn't really come up with much so far.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
It could be that the size of your gas line is not sufficient for the volume of gas needed when they are on high fire.

What are their BTU's, and what size line is feeding them? What is the volume rating on the regulators involved? I'd expect the ones at the appliances would be adequate for the burner, since they manufacturer should know what's required, but the one upstream may not be able to handle the volume needed, or the supply pipe may be too small or long.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks