go_hercules
Member
Some of you may find this interesting, others may not, so here goes. We all know to set the initial pressure on the expansion tank "around" the same as static water pressure. You read some arguments that it should be a little higher or a little lower, etc. So, after a long shower, I monitored the house water pressure while the water heater ran. It started at 60 psi. Almost immediately, it started rising slowly. By the time the water heater shut back off, the static water pressure had risen to about 72 psi. Acceptable for sure, but why the difference. I read all sorts of theories (too low initial pressure = low acceptance volume, too high initial pressure = initial rise until pressures equalize, etc.) So here is what I did. I did the whole test over the next day, but this time just after the water heater shut off and the pressure had risen to about 72 psi, I released just a little air from the expansion tank until the static water pressure fell to 60 psi. I did the whole routine over, and this time the pressure stayed at 60 psi even after the water heater cycled. So I think I found the "magic" setting for initial air pressure. When I get a chance, maybe tomorrow, I will drain down the hot water so I can check what actual air pressure I ended up with. Definitely BELOW the water pressure, but not sure how much. I think in most situations, anywhere reasonably close to static water pressure will work good enough to protect pipes and prevent T/P tripping, but this just seems to be more accurate.