I understand that a knock arrestor has a piston and O rings inside the chamber that compress the air above it to arrest the sudden spike in water pressure. If you remove the arrestor and push on the bottom of that piston, should you be able to feel it move inward and then return? Would that be a valid check to see if it is still working? I realize you could also maybe hear if it is no good anymore, but I'd like to know if this is also a test.

PS this would be in a home laundry..........about a $11 to $20 item.
 

James Henry

In the Trades
Messages
1,580
Reaction score
404
Points
83
Location
Billings, Montana.
The spring most likely wouldn't fail it would be water leaking by the o-rings which would eliminate the air chamber. So no, I would say that would not be a suitable test.
 

LLigetfa

DIYer, not in the trades
Messages
7,508
Reaction score
581
Points
113
Location
NW Ontario, Canada
Test it by replacing or comparing to a known good unit. I don't know how much pressure they are precharged to but suspect it would be too much to move the piston by hand. I doubt they have a mechanical spring.
 

Reach4

Well-Known Member
Messages
38,931
Reaction score
4,449
Points
113
Location
IL
I think your plan makes sense, but I don't know if there is some pitfall, such as the bottom of the piston being too delicate, or the the path not being straight or big-enough.

Force required would be considerable I think.
water-hammer-arrestor-function.jpg
 

SteelerEd

New Member
Messages
4
Reaction score
0
Points
1
Location
14068
Well I got them yesterday and using a piece of roundstock to try to move the piston was not possible. I really pushed hard and neither one would budge. Makes me wonder how much pressure they charge them with. I'd say I pushed with more then 100 pounds. What is the spike on a typical copper tubing system on a residental system with washing machine solenoids?
 

Reach4

Well-Known Member
Messages
38,931
Reaction score
4,449
Points
113
Location
IL
I would think maybe 60 psi. I did some looking, and I think that was the highest number I saw.

Now if we presume the cross sectional area is 0.5 square inches, that would correspond to 30 pounds of force to get started, and maybe 40 to get a noticeable displacement.
 
Last edited:

LLigetfa

DIYer, not in the trades
Messages
7,508
Reaction score
581
Points
113
Location
NW Ontario, Canada
I tested one I had laying around and it was too easy to depress the piston. In fact there was no precharge on it and the piston did not return all the way back.
 

SteelerEd

New Member
Messages
4
Reaction score
0
Points
1
Location
14068
Well, I have them on hand now so I'm going to mount them in a vertical position. If they fail I'll go back to the 2 foot copper tubing that I had before, only this time I'll put some valves on the supply lines. Maybe twice a year I'll just close them and drain the 2 footers to recharge them. That way I know it is working.

Would there be an advantage to using 3/4 or 1 inch pipe instead?
 

Kreemoweet

In the Trades
Messages
754
Reaction score
66
Points
28
Location
Seattle. WA
SteelerEd said:
Would there be an advantage to using 3/4 or 1 inch pipe instead?

The bigger the pipe diameter, the greater the capacity to absorb shock, and the longer it takes to lose the air.
Most of these little plunger-type arrestors I've dealt with barely work when new, and fail completely soon after.
 

Reach4

Well-Known Member
Messages
38,931
Reaction score
4,449
Points
113
Location
IL
Well, I have them on hand now so I'm going to mount them in a vertical position. If they fail I'll go back to the 2 foot copper tubing that I had before, only this time I'll put some valves on the supply lines. Maybe twice a year I'll just close them and drain the 2 footers to recharge them. That way I know it is working.

Would there be an advantage to using 3/4 or 1 inch pipe instead?

For your homemade water hammer arrestors, you would open the valves to drain the water, to admit air.
 

John Gayewski

In the Trades
Messages
4,372
Reaction score
1,352
Points
113
Location
Iowa
If you look way back in the code when pipe was legal to use as Janet arrestors the sizing for them was ridiculous. They have to be huge to really be proper.
 