Hello! I'm desperate for some advice. We haven't had water for a week and it's nearly impossible to find a professional to service our house (we live in the mountains and there is only a limited number of professional companies within 1 1/2 - 2 hrs of us). I had 2 local guys working on it this week and they couldn't figure it out. Here's an overview of the situation and our setup. Please forgive me if I incorrectly label something. I'm not an electrician, mechanic, well professional, etc. I work in Human Resources. LOL.

Last week Saturday, our dog dug the cover off of the junction box that is underground next to our cistern in the middle of the yard. When I inspected the damage, there was 1 wire nut on the ground and three exposed wires. Fast forward to this past Monday and we noticed that our jet pump (in the mechanical room in our house) was running on almost 0 PSI. At that point, we turned off the Well and Pressure Pump switches as to not damage the system. I hadn't noticed at the time, but our Pumptech was also completely dead - no power.

After some testing, it turns out that the exposed wires in the junction box were to the float switch (a yellow and black wire in a black sheath) and a hot wire that powers the pumptech. Logic would tell me that all of these wires need to be reconnected but to where???? That's what no one can figure out. The junction box is filled with wires that run underground and I have no idea where they all lead. I'll post some pictures and maybe, just maybe, someone on here can help me. I would LOVE to take a proper shower one of these days!!
65557533106__E89633A2-AB24-48AE-8352-3A6571580AEC.jpg
IMG_1953.jpg
IMG_1955.jpg
IMG_1941.jpg
65557697639__63BB88A2-5EDF-466F-8BDB-69566D32396E.jpg
65557691711__4FE88D4D-D99E-4A83-BCAC-FEF93CF0BC2D.jpg
65557687580__52DBA6AA-5CA1-464C-AA17-49D4EB0295E6.jpg
65557545748__81E8E530-180E-4FCA-B9AD-A5712E0BD4C5.jpg
IMG_1943.jpg
 

Attachments

  • IMG_1941.jpg
    IMG_1941.jpg
    122.2 KB · Views: 136

Reach4

Well-Known Member
Messages
38,902
Reaction score
4,436
Points
113
Location
IL
After some testing, it turns out that the exposed wires in the junction box were to the float switch (a yellow and black wire in a black sheath)
So the float switch is in the cistern, and the black and white cable are the only wires going to the cistern.

There are 3 or 4 wires going down the well -- which?

Gray box says Kralox on the front and has something inside. That could be a relay/contactor that actually controls the well pump, itself being switched by the float switch.

and a hot wire that powers the pumptech.
Are you saying that you think that that hot provides power to the Pumptech? Seems like power would go from the house to the well and cistern.

Then the jet pump is controlled by a pressure switch at the pressure tank, and that area is not in the photos.
 

Danielle Achziger

New Member
Messages
3
Reaction score
0
Points
1
Location
Norwood, CO
So the float switch is in the cistern, and the black and white cable are the only wires going to the cistern.

There are 3 or 4 wires going down the well -- which?

Gray box says Kralox on the front and has something inside. That could be a relay/contactor that actually controls the well pump, itself being switched by the float switch.


Are you saying that you think that that hot provides power to the Pumptech? Seems like power would go from the house to the well and cistern.

Then the jet pump is controlled by a pressure switch at the pressure tank, and that area is not in the photos.

The float switch is in the cistern which only contains the cable to the float. The well is located somewhere else. The white wire is buried underground but I'm not sure where that goes. All of these wires are buried underground. When we flipped the breaker to the 'pump' (#10 in the picture), the hot wire lost power. I believe that's the power to the pumptech. There is a separate breaker for the pressure tank and well.
 

Attachments

  • 65557608619__1F703DF3-C856-43E2-917A-B756E717F479.jpg
    65557608619__1F703DF3-C856-43E2-917A-B756E717F479.jpg
    20.4 KB · Views: 151
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks