LauraH
New Member
So we have decided to have a tankless water heater installed, Rheem model: RTGH-95DVLN-1 (link to specs, features and docs). I contacted our gas company PSNC Energy here in Mooresville, NC, to ask them for a meter upgrade. We currently have the AC-250 meter with 1/2" outlet with 2 psig service. The half inch pipe coming from the meter and entering our crawl space is split into two additional 1/2" gas pipes. One of them travels 15' to the HVAC system under our crawl space that is rated at 70,000 BTUS. The second pipe travels about 30' (15' of it in the crawl space then up another 15' to a utility closet on the second floor inside our home to the second HVAC unit, also rated at 70,000 BTUs. The Rheem model requires 199,000 BTUs and has a gas inlet of 3/4".
So by my calculations: 70,000 + 70,000 + 199,000 = 340,000 BTUs, thus my request for an upgraded meter with a 3/4" outlet from the meter. So after my call, they decide to send out a representative to evaluate our needs. (UGH!) He says the meter does not need to be upgraded that all three appliances will run just fine on the 250 meter, and that he doesn't need to modify the 1/2" outlet from the meter, he just needs to tee off the existing 1/2" piping with a 3/4" pipe near the expected location/install point of the tankless water heater.
There are two locations we are looking at. The first one is in the same utility closet on the second floor with the HVAC (3 feet of clearance all around), so that would mean a 30' run of pipe. Or the second location is in the garage on the other side of the house which would mean a 60' run of pipe.
Here are my questions:
1. Is a 250,000 BTU supply meter good enough? I expect there will be many times in the winter months when all three appliances would be running at the same time.
2. Can you go from a smaller pipe (1/2") to a larger pipe (3/4") on a 2 psig system and not starve the tankless water heater, or cause other problems that this layperson (me) isn't aware of?
3. If what he is saying about the sizing of the pipe is correct, at what point on the piping run should he be switching from 1/2" pipe to 3/4" pipe.
I'm having serious doubts about this "expert" since he seems to be saying things that don't seem to jive with what I've been reading over the past several months. Hoping some of you experienced and trained experts can shine some light on this and set my mind at ease with what this PSNC representative is telling me.
Thank you so much in advanced for your help. Laura
So by my calculations: 70,000 + 70,000 + 199,000 = 340,000 BTUs, thus my request for an upgraded meter with a 3/4" outlet from the meter. So after my call, they decide to send out a representative to evaluate our needs. (UGH!) He says the meter does not need to be upgraded that all three appliances will run just fine on the 250 meter, and that he doesn't need to modify the 1/2" outlet from the meter, he just needs to tee off the existing 1/2" piping with a 3/4" pipe near the expected location/install point of the tankless water heater.
There are two locations we are looking at. The first one is in the same utility closet on the second floor with the HVAC (3 feet of clearance all around), so that would mean a 30' run of pipe. Or the second location is in the garage on the other side of the house which would mean a 60' run of pipe.
Here are my questions:
1. Is a 250,000 BTU supply meter good enough? I expect there will be many times in the winter months when all three appliances would be running at the same time.
2. Can you go from a smaller pipe (1/2") to a larger pipe (3/4") on a 2 psig system and not starve the tankless water heater, or cause other problems that this layperson (me) isn't aware of?
3. If what he is saying about the sizing of the pipe is correct, at what point on the piping run should he be switching from 1/2" pipe to 3/4" pipe.
I'm having serious doubts about this "expert" since he seems to be saying things that don't seem to jive with what I've been reading over the past several months. Hoping some of you experienced and trained experts can shine some light on this and set my mind at ease with what this PSNC representative is telling me.
Thank you so much in advanced for your help. Laura