3/4 meter to 1.5" main line - where to install PRV and Backflow preventer?

Users who are viewing this thread

PeterT

New Member
Messages
26
Reaction score
1
Points
3
Location
Los Angeles
Existing meter is 3/4". The house main line (250' long) should be 1.50" based on fixture # and run length. Pressure and flow are fine presently from the 3/4" meter via a 1" a pvc main line.

As the yard is torn up, I'm going to install a new 1.5" main line in case there's a need to upgrade the water meter in the future. Presently, there's a 1" PRV reducing pressure from 80psi to 60psi.

Question: can I install a 1" PRV and a 1" backflow valve just after the 3/4" meter and on a 1" pipe but before the transition to the 1.5" main line? Any reason why this isn't advisable other than a future meter upgrade would require them to be upsized? Does it make a difference installing the PRV so far from the house presuming I just run the pressure a bit higher to compensate for the long run?

1.5" PRV's and 1.5" backflow prevention valves get very expensive and may actually never be needed. But I don't know if their 1" size will somehow limit flow even though the meter is only 3/4".

thanks.
 

Reach4

Well-Known Member
Messages
41,297
Reaction score
4,974
Points
113
Location
IL

Question: can I install a 1" PRV and a 1" backflow valve just after the 3/4" meter and on a 1" pipe but before the transition to the 1.5" main line? Any reason why this isn't advisable other than a future meter upgrade would require them to be upsized? Does it make a difference installing the PRV so far from the house presuming I just run the pressure a bit higher to compensate for the long run?
Installing the PRV at the house is better for regulation.
 

PeterT

New Member
Messages
26
Reaction score
1
Points
3
Location
Los Angeles


Installing the PRV at the house is better for regulation.

agreed, can I install a 1" PRV where the 1.5" transitions back to 1" pex in the garage or does the PRV need to be 1.5"?

Also, I'm thinking it may be better to have the sprinkler system unregulated (meaning the PRV can go in the garage vs outdoors) since sprinklers don't have the same high pressure risk factors as an indoor pipe.
 

wwhitney

In the Trades
Messages
7,249
Reaction score
2,065
Points
113
Location
Berkeley, CA
agreed, can I install a 1" PRV where the 1.5" transitions back to 1" pex in the garage
Sure.

PRVs are sized based on the expected flow and the acceptable pressure loss through the PRV at that flow. That is, if your PRV sees 80 psi static (= no flow) on its inlet, it will keep the outlet pressure at 60 psi. But if you draw 10 gpm, say, through the PRV, the outlet pressure of the PRV will drop a little, maybe a few psi? If you use a large PRV, you can get more flow through the PRV with less pressure drop.

So if a 1" PRV is adequately sized for your flow, and you need to install it in a 1.5" line that was upsized due to distance, there's no harm in just downsizing to 1" for a foot or two so that you can connect a 1" PRV.

Cheers, Wayne
 

PeterT

New Member
Messages
26
Reaction score
1
Points
3
Location
Los Angeles
Sure.

PRVs are sized based on the expected flow and the acceptable pressure loss through the PRV at that flow. That is, if your PRV sees 80 psi static (= no flow) on its inlet, it will keep the outlet pressure at 60 psi. But if you draw 10 gpm, say, through the PRV, the outlet pressure of the PRV will drop a little, maybe a few psi? If you use a large PRV, you can get more flow through the PRV with less pressure drop.

So if a 1" PRV is adequately sized for your flow, and you need to install it in a 1.5" line that was upsized due to distance, there's no harm in just downsizing to 1" for a foot or two so that you can connect a 1" PRV.

Cheers, Wayne
thanks Wayne.

Ditto for the back flow prevention valve at the meter? Can I use a 1" backflow prevention valve before upsizing to 1.5" pipe for the long run? I need to keep the BFP near the meter as its the highest point in the yard.
 