Flex conduit through roof

Users who are viewing this thread

pls2000

New Member
Messages
7
Reaction score
0
Points
1
Location
Phoenix, AZ
I'm in the process of replacing my roof mounted air conditioner. I just discovered the that original installer (for a previous owner) ran flex conduit through the roof to provide power.

What the did was to punch a hold in the roof, drag the conduit through it, and slather roofing tar over the hole. Now that area leaks.

Is the a way to provide proper protection and flashing for flex conduit penetrating a roof? Everything I've ever seen or done uses rigid conduit for the actual penetration, usual with a small junction box or pull box at the top.

Thanks,
++PLS
 

Stuff

Well-Known Member
Messages
1,221
Reaction score
131
Points
63
Location
Pennsylvania
First - traditional FMC (flexible metal conduit) is not permitted since it goes outdoors which is a wet location. Liquidtight (plastic/nylon coated) is what is allowed outdoors.

What about sunlight resistant UF cable instead? Then run it over the roof edge and do a wall penetration.
 

Reach4

Well-Known Member
Messages
41,353
Reaction score
4,985
Points
113
Location
IL
Is the a way to provide proper protection and flashing for flex conduit penetrating a roof? Everything I've ever seen or done uses rigid conduit for the actual penetration, usual with a small junction box or pull box at the top.
Another idea... I think a roof penetration, with a roof flashing replacing a shingle, stops rain at the roof.

Then maybe a 1-1/4 weatherhead could go atop the conduit. While 1-1/4 was the smallest I saw, there could be smaller. But their are other options... http://www.quickmountpv.com/products/conduit-penetration-flashing.html?cur=0 has this picture:
prodImg1-CPC.jpg


This is harder than the UV-resistant UF around the roof edge.
 
Last edited:

Norcal01

Member
Messages
63
Reaction score
6
Points
8
Look for a solar flashing perfect for 1/2 sealtite, I would avoid any roof jacks with a rubber seal as they are prone to failure.
 