Expansion Tank install options with up connection

Discussion in 'Water Heater Forum, Tanks' started by Eljay, Jan 12, 2019.

  1. Eljay

    Eljay New Member

    Joined:
    Dec 7, 2018
    Location:
    Southwestern US
    We moved into a home with a PRV but no water heater expansion tank. Leaks around the house have made installing an expansion tank a priority. Better late than never.

    I see many folks installing tanks horizontally with/without straps or vertically with the connection down. I'd just like to play it as safe as possible and install it vertically with connection up. Making it easier to switch out tanks without taking a bath is an added bonus.

    Question 1: What do you all think about the installation options below?

    Option A (Blue line): Copper pipe with a straight shot from the cold water line completely across the top of the water heater and then downward to the expansion tank. I don't have much experience running copper pipe for water. But I assume that this would be too long of a run without any added support. I would use a couple of shelf brackets (something like this at home depot) installed at each two available wall studs.
    The pipe would be secured to the shelf brackets using copper tube straps.

    Option B (Green line): Copper pipe runs along the wall. A 2"x6" would be installed horizontally spanning two studs along the wall. Copper tube straps (home depot) would secure the pipe to the 2"x6" at two points.

    Option C (not pictured): Run corrugated copper or steel connectors.

    [​IMG]

    In all scenarios, I'd secure the expansion tank to the wall using one of these brackets:

    Storm King Hydroclaw (supplyhouse)
    or
    Holdrite Quickstrap (supplyhouse)


    I assume Option B (green line) is preferred since it will provide the most support when the bladder fails?


    Question 2: A MIP adapter is currently installed on the cold water supply shutoff valve allowing connection to the water heater with corrugated steel flexible hoses. Ideally, I know it should be removed. But I don't have much experience unsoldering copper fittings, especially in such an awkward space so close to the wall. Could I just screw on a FIP adapter and go from there?
     
  2. Master Plumber Mark

    Master Plumber Mark Sensitivity trainer and plumber of mens souls

    Joined:
    Feb 6, 2005
    Occupation:
    Sensitivity trainer.. plumber of mens souls
    Location:
    indianapolis indiana - land of the free, home of
    you need to put up some pictures....
    if you dont know how to solder then its gonna be
    a struggle to get it the way you want


    their are many ways to support a thermal expansion tank
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. Eljay

    Eljay New Member

    Joined:
    Dec 7, 2018
    Location:
    Southwestern US
    I can solder. I just don't claim to be good at it. o_O:eek:

    I've recently soldered about a dozen joints installing a water softener with 1" pipe. The joints definitely aren't pretty. But they don't leak.

    Do these pictures help?

    [​IMG]

    [​IMG]
     
  5. Master Plumber Mark

    Master Plumber Mark Sensitivity trainer and plumber of mens souls

    Joined:
    Feb 6, 2005
    Occupation:
    Sensitivity trainer.. plumber of mens souls
    Location:
    indianapolis indiana - land of the free, home of
    If you are saving the water heater this is pretty easy peasy... The heater has those flex
    connectors on it and you should just have to un hook the cold side and install a 3/4 brass tee
    and then some brass nipples and set it up something like in the picture below...

    the work I am looking at is pretty rough looking, but the flex connectors are ok, just a little
    shabby in appearance... We have used hundreds of them over the years and they seem to
    work very well....

    the t+p drain looks rough with the flex connector in the line.... I suppose it will work properly
    but it looks like crap....

    If your flu pipe off the heater is aluminium dryer vent pipe it ought to be changed out to heavier guage
    steel flu pipe...

    look at my web site on yelp and you will see some installs with the tanks and tees

    https://www.yelp.com/biz/weilhammer-plumbing-indianapolis-3



    Tank note that we installed this therm tank with galvanized pipe instead of brass fittings
    I suggest the brass fittings will last longer... we have switched to the brass ones
    you support the therm tank arm with
    a wedge between the top of the heater and the arm.....

    [​IMG]
     
    Eljay likes this.
  6. Eljay

    Eljay New Member

    Joined:
    Dec 7, 2018
    Location:
    Southwestern US
    Thanks, Mark.

    Won't the the brass fittings still eventually corrode at the water heater? If they don't leak, would stainless steel 304 or 316 threaded fittings be better (though I have read that there are issues with galling)? I had seen pictures of folks using fittings at the water heater with and without a wedge to support the fittings. I hadn't seriously considered going that route since I was worried that the water heater wasn't designed to support 50+ lbs once the bladder fails and tank fills up with water. But if the pros have been doing it this way, I guess I shouldn't worry.

    My original idea is similar to this.
    [​IMG]

    But I also wanted to support the pipe as well using tube straps and the like. I'm pretty green when it comes to this plumbing stuff. But my work has taught me to eliminate single points of failure when possible. I liked the idea of clamping the expansion tank to the wall. If that somehow fails, I also thought it might be a good idea to support the pipes as much as possible and screw them to the wall. It's fairly common for us to not be home for few weeks. I'd hate to come back to a flooded house if we forgot to shut off the water before leaving.
     
  7. Master Plumber Mark

    Master Plumber Mark Sensitivity trainer and plumber of mens souls

    Joined:
    Feb 6, 2005
    Occupation:
    Sensitivity trainer.. plumber of mens souls
    Location:
    indianapolis indiana - land of the free, home of
    anything to support the tank will work... and any place you have a joint
    it potential for a leak sometime down the road...

    you can do this any way you wish, the brass tee off the top of the
    heater is about the easiest way to do it without making a contest out of it....
    This tee will probably last 10 times longer than the heater will and of course
    their are old galvanized tees that are over 100 years old still working great out there somewhere.
    I think as long as you put a shim under the arm to support the weight I dont think its an issue

    carry on as you see fit.....
     
    Eljay likes this.
  8. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    Avoid galvanized fittings, but the tank can actually be mounted in lots of places in any orientation. As long as it's between the WH and the cold shutoff, it should be fine. You do want to be able to access the air valve on the bottom in case it needs a little fill up sometime later.
     
    Eljay likes this.
Similar Threads: Expansion Tank
Forum Title Date
Water Heater Forum, Tanks Thermal Expansion Tank Installation Oct 1, 2018
Water Heater Forum, Tanks What is failing? TRP valve or expansion tank or both? Jul 21, 2018
Water Heater Forum, Tanks Plumber recommending not to install expansion tank with new heater Jul 13, 2018
Water Heater Forum, Tanks What pressure in HW heater expansion tank? Apr 19, 2018
Water Heater Forum, Tanks Expansion tank on hot water line? Cold Apr 7, 2018

Share This Page