I suggest a 20 amp circuit breaker, #12 copper conductors, and a 30A fused disconnect (the smallest size). That way if the nameplate really says "max fuse" instead of "max breaker," you can change the fuses to 20A. Note that a 30" wide by 36" area in front of the disconnect has to remain clear, so put the unit to the side of the disconnect, not in front of it.
Cheers, Wayne
NM (romex) is OK inside your house, inside an enclosure outdoors, and within your siding.
So if you come into the back of your disconnect mounted on the siding, you can run NM all the way into the disconnect. If you enter the disconnect in any other fashion, you'd need to transition inside from NM to an outdoor wiring method.
Load side, yes, you use a whip with THWN conductors.
Cheers, Wayne
Option 1: Use UF cable from the panel to the disconnect box. That way you can run it outside for the vertical jog up to your disconnect box. You might want to use a conduit sleeve to protect the vertical leg. Avoids a splice.
Option 2: Set an exterior junction box at the location you come out of the house, enter it from the back with NM. Splice to individual conductors there. Use a short conduit run up to the disconnect.
As to the wires, that's a good choice if it is stranded. Solid is allowed, but I think it would make pulling the wires through the LFNC harder, particularly with the angle connector. Or maybe it would be OK.
Cheers, Wayne
Since the unit is 120V, you don't want a fuse in the neutral conductor. Since most (all?) disconnects are two poles, you'd just one one side with the ungrounded conductor, and splice the neutral conductor straight through. The other side would be unused.
If the second item really is a one pole disconnect, meaning it only has one fuse, and maybe has a set of lugs insulated from the case for splicing the neutral, that would be convenient. But if you look up the manufacturer part number given, there's no discussion of that. So I think that's just a typo on Lowe's website, and the two items are basically the same.
Your other option is to get a copy of the name plate (or wait until you have the unit), and see if it really says "Max 20A Fuses" or instead uses the word OCPD or Breaker. In the latter case you could use an unfused disconnect. I'd be inclined to go that way.
Cheers, Wayne
If unfused, sure. 60 amp may be the smallest size they make.
If fused, I'm not sure, there's a question of whether the bigger size will take a 20 amp fuse if need be. I'm guessing 30 amp and under is one physical size, and 31-60 is a different physical size. But in that case they probably make reducers that allow the physically smaller fuse to fit in the larger fuse holder.
Cheers, Wayne