thomase00
New Member
I looked more closely at the Manual-J report generated by HVAC-Calc and found some issues:
1.) Since I was using this primarily to calculate cooling load (heat gain) for my central AC, and my central AC has ducts (though insulated) in unconditioned attic space, the heat loss calculation ALSO included duct losses, assuming that the attic is at the outside temperature during heating season. These losses add up to 8K BTU, which I think is a bit much considering that I don't actually have air moving through the ducts during the heating season.
2.) For my brick fireplace, the software gave me 3 choices for "leakiness": poor, average, and good. In the winter, the bricks are cool to the touch and there can sometimes be a little draft coming from the hair-thin gaps between the hearth and the flooring. Not being sure what poor/average/good meant, I choose poor to be conservative. This had ZERO effect on the cooling load, but added 26K BTU to the heating load! I'm guessing the software assumes that "poor" means "wide open damper sucking heated air out of the house"! Also, when this whole project is done, the brick fireplace will be gone!
3.) Again, knowing that some of my windows are drafty, and hearing not so great things about the builder, I chose "average" tightness which amounts to 0.7 air exchanges per hour in the winter. This results in 32K of heat loss! Obviously, this is a HUGE factor, so it greatly skews the result if my guess is off. Unfortunately, I never got an accurate measure of ACH when MassSave came to do a blower door test. They just gave me some measure of the before/after difference after sealing my attic, and it WASN'T in units of air exchanges per hour.
So, out of the 91K BTU of estimated heat loss, 66K is due to what essentially amounts to a guess!
Edit: Also, the heat gain calculation (for cooling load) included about 5K BTU from occupants and appliances, and this was not automatically subtracted from the heating load.
1.) Since I was using this primarily to calculate cooling load (heat gain) for my central AC, and my central AC has ducts (though insulated) in unconditioned attic space, the heat loss calculation ALSO included duct losses, assuming that the attic is at the outside temperature during heating season. These losses add up to 8K BTU, which I think is a bit much considering that I don't actually have air moving through the ducts during the heating season.
2.) For my brick fireplace, the software gave me 3 choices for "leakiness": poor, average, and good. In the winter, the bricks are cool to the touch and there can sometimes be a little draft coming from the hair-thin gaps between the hearth and the flooring. Not being sure what poor/average/good meant, I choose poor to be conservative. This had ZERO effect on the cooling load, but added 26K BTU to the heating load! I'm guessing the software assumes that "poor" means "wide open damper sucking heated air out of the house"! Also, when this whole project is done, the brick fireplace will be gone!
3.) Again, knowing that some of my windows are drafty, and hearing not so great things about the builder, I chose "average" tightness which amounts to 0.7 air exchanges per hour in the winter. This results in 32K of heat loss! Obviously, this is a HUGE factor, so it greatly skews the result if my guess is off. Unfortunately, I never got an accurate measure of ACH when MassSave came to do a blower door test. They just gave me some measure of the before/after difference after sealing my attic, and it WASN'T in units of air exchanges per hour.
So, out of the 91K BTU of estimated heat loss, 66K is due to what essentially amounts to a guess!
Edit: Also, the heat gain calculation (for cooling load) included about 5K BTU from occupants and appliances, and this was not automatically subtracted from the heating load.