Hello All,
I’m taking on a bathroom addition in my basement(will be bathroom #2 in the house) and am getting mixed feedback from the plumbers I’m talking to about size of underground piping. For my area we are subject to 2015 IPC/IRC/IBC.
Does anyone see any issues with the layout I’m proposing or have any thoughts on the pipe sizing questions?
I’m taking on a bathroom addition in my basement(will be bathroom #2 in the house) and am getting mixed feedback from the plumbers I’m talking to about size of underground piping. For my area we are subject to 2015 IPC/IRC/IBC.
- The existing concrete has been broken away to reveal a very shallow connection to the outgoing lateral (4” cast). At the completion of the underground plumbing my intent is to add 1” – 1.5” of leveler to the area to level and add meat to the slab.
- 3pc bath to be added (shower), along with a new laundry sink and re-establishment of an existing floor drain and washing machine drain.
- I have a new 2” vent line that installs from the basement joist space, through a wall cavity on the main floor, through attic and out the roof, with a single 45deg offset in the attic space
- I have spoken with three plumbers and all of them have said that my run to the proposed toilet will need to be in 4” because it’s underground. I have found some other threads on this site that indicate that 3” is acceptable, and I cannot find anything in the code that mandates 4” (or anything that differentiates sizing for above versus underground for that matter). Due to the shallowness of the connection to the lateral I am trying to reduce my pipe diameters and underground run lengths as much as allowable.
- Similarly, they are also saying that the modified floor drain must be a minimum 3” instead of the 2” that I have in my plans. Again, everything I see in 2015 IPC indicates to me that 2” is to code.
- What I can see for the DFU limitations per branch I feel that my attached design hits the mark, and I have a number of 2” vents that would route up above and connect to the new 2” to exterior that is installed.
Does anyone see any issues with the layout I’m proposing or have any thoughts on the pipe sizing questions?