30 Amp Generator output into a 50 Amp inlet.
Jman2012a
I have an existing generator that has a 30 amp outlet, however, my house I recently purchased has a 50 amp power inlet box. The 50 amp circuit breaker in the box has an interlock, so we have protection from that stand point. My question is can I use my generator that feeds 30 amps to the 50 amp power inlet box using an adapter from a legitimate manufacture, such as Westinghouse? The proper generator adapter would be male on the 30 amp side and female on the 50 amp, so it would not be a suicide adapter. It sounds logical to be able to do it safely since the power source (30 amp from generator) is less than the breaker/wiring (50 amp) that it is feeding into. I wanted to try to avoid having it rewired to a 30 amp power inlet. Also, in the future I might buy a different generator that has a 50 amp outlet.
wwhitney
Berkeley, CA
Assuming they are both 120/240 (NEMA 14 or L14) I see no safety issue, just a lower threshold for overloading the generator.
You do need to confirm the generator bonding matches the specifications that should be posted by the inlet. With a breaker interlock, that means that the generator neutral should not be bonded to its ground (frame); whereas on a generator used as a standalone source, its neutral and ground should be bonded. So depending on your generator, it will may be hard to convert it back and forth for the two use cases.