GFCI Wiring Question

Users who are viewing this thread

Martina

Member
Messages
79
Reaction score
2
Points
8
Location
Round Rock, Texas
Hello, everyone!

I was mapping our exterior home circuit today to see about adding additional outlets and came across and unfamiliar wiring scenario that I’d like to get some clarification on. The entire 20-amp circuit consists of six receptacles (one GFCI located inside our garage and five standard outlets distributed along the exterior of our home). The 12-gauge wire runs from the main panel directly to the GFCI, making it the first in line, which I know is correct. However, to my surprise it appears that from the GFCI, the circuit branches off in two directions (see attached drawing). I was always under the impression that the GFCI is the first in line and from there, everything proceeds down-circuit in a single direction. Based on what I’ve found in the attic, however, that doesn’t seem to be the case. I have a total of three 12-gauge wires running through the top plate- one that runs from the main panel to the GFCI, the second one feeds an exterior outlet on the southside of our home and the third one travels to an exterior outlet on the eastside. Is this an acceptable wiring method?

Thanks in advance for any forthcoming responses.

Martina
 

Attachments

  • GFCI.jpg
    GFCI.jpg
    32.1 KB · Views: 133

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
That's fine. Electrically, there's little difference between one daisy chain downstream of the GFCI, and two daisy chains.

Physically, a single daisy chain could be connected with the two conductor cable going to the first downstream receptacle terminated directly to the GFCI LOAD terminals. Since the GFCI LOAD terminals each accept up to 2 conductors typically, you can supply two separate daisy chains without requiring any pigtails or extra connectors (e.g. wire nuts). If you exceed 2 daisy chains supplied, you'd need pigtails and extra connectors, but if your box is big enough to satisfy the box fill requirements, you could supply as many cables as you like.

Cheers, Wayne
 

Martina

Member
Messages
79
Reaction score
2
Points
8
Location
Round Rock, Texas
That's fine. Electrically, there's little difference between one daisy chain downstream of the GFCI, and two daisy chains.

Physically, a single daisy chain could be connected with the two conductor cable going to the first downstream receptacle terminated directly to the GFCI LOAD terminals. Since the GFCI LOAD terminals each accept up to 2 conductors typically, you can supply two separate daisy chains without requiring any pigtails or extra connectors (e.g. wire nuts). If you exceed 2 daisy chains supplied, you'd need pigtails and extra connectors, but if your box is big enough to satisfy the box fill requirements, you could supply as many cables as you like.

Cheers, Wayne
Thank you for your prompt reply and all the additional information! Always learning something new. :)

Have a great week, Wayne!
 

Reach4

Well-Known Member
Messages
38,898
Reaction score
4,436
Points
113
Location
IL
With 1 GFCI feeding 5 outdoor outlets, I would think there could be a fair amount of trips in rainy weather. Check the covers on outdoor outlets to make sure they are not going to leak.

At least you are not in the highest humidity part of the state.
 

Martina

Member
Messages
79
Reaction score
2
Points
8
Location
Round Rock, Texas
With 1 GFCI feeding 5 outdoor outlets, I would think there could be a fair amount of trips in rainy weather. Check the covers on outdoor outlets to make sure they are not going to leak.

At least you are not in the highest humidity part of the state.
Great point as we did experience issues with tripping in the past, especially during the winter. I have since installed bubble covers on all the exterior outlets and things have been quiet since then.

Thanks for your input!

Martina
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks