Can i vent a shower and a bathtub on the same 1.5" vent? I have a back to back shower/tub currently and i am remodeling the shower side. I am hoping i can combine the vents for each into one. Something like the image attached? Thanks!
 

Attachments

  • vent.png
    vent.png
    40.9 KB · Views: 259

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Almost, but not quite. Below that top connection, it's a drain and can't be used as a vent. But, if you bring a vent up from the lower one, you can then attach it to the vent above so you don't need to run two vent lines all the way up. Normally, you'd revent the line 42" above the floor, or 6" above the height of the highest drain (the 42" comes from a potential 36" counter plus the 6").
 

TheGewp

Member
Messages
73
Reaction score
1
Points
8
Location
Washington County, OR
What if i used a double fixture tee instead of stacking them? Also, off topic, why are bathtubs usually shown with 1.5" pipe and showers with 2"? Can i use 2" on a tub? Thanks!!
 

Reach4

Well-Known Member
Messages
38,899
Reaction score
4,436
Points
113
Location
IL
A tub has some storage so if the drain goes slower, there is time to empty the tub. A shower would overflow quickly.

Yes, you can use 2 on a tub.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
There may be a smaller selection of drains in 2" than 1.5", but they're available.
 

Reach4

Well-Known Member
Messages
38,899
Reaction score
4,436
Points
113
Location
IL
Makes sense. How about using a tee in the image i attached?
I think you could use a double santee, but better would be that double fixture fitting that you mentioned. Use a 2x2x2x2 and reduce for the tub somewhere along the line... maybe at the trap, or even at the double fixture fitting.

What I am not sure of is whether there is a problem with your original drawing with two santees.
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Note that the trap arm cannot go down (beyond the nominal 1/4"/foot slope) until it is vented.
 

TheGewp

Member
Messages
73
Reaction score
1
Points
8
Location
Washington County, OR
Basically i would like to do this: https://terrylove.com/images/double_lav_rough_2.jpg with a shower and a tub that are back to back. It is the only way to combine the vents without ripping a wall apart. I am trying to remove the shower vent to make room for a niche in the shower wall and avoid working around a floor joist. Can i use a 2x2x2x2 double fixture tee and size down to a 1.5" line for the tub and vent and leave it at 2" for the shower and drain to the stack? Thanks!
 

TheGewp

Member
Messages
73
Reaction score
1
Points
8
Location
Washington County, OR
Finally got to this, everything look OK? I will add straps when i get the floor supports in. The nearest 2" nub will go to a shower. Thanks!

2020-01-26 19.13.09.jpg
 

Plumber01

In the Trades
Messages
108
Reaction score
17
Points
18
Location
Washington
Too many turns in the trap arm. Cant exceed 90 degrees without a cleanout on a trap arm with 2" pipe or less.

Looks like you could have configured the double fixture tee better to avoid that.
 

TheGewp

Member
Messages
73
Reaction score
1
Points
8
Location
Washington County, OR
Too many turns in the trap arm. Cant exceed 90 degrees without a cleanout on a trap arm with 2" pipe or less.

So replacing this 90 with a combi with a clean out cap should do the trick?

2020-01-26 19.13.09_2.jpg


The shower drain would need 2 90's if i rotated the tee 90 degrees, is there a better way other than that? Thanks!
 

James Henry

In the Trades
Messages
1,579
Reaction score
404
Points
83
Location
Billings, Montana.
Can i vent a shower and a bathtub on the same 1.5" vent? I have a back to back shower/tub currently and i am remodeling the shower side. I am hoping i can combine the vents for each into one. Something like the image attached? Thanks!


You could have stacked your fixtures like you had in your original drawing. Either way code says you need a 2" drain.
 
Last edited:

TheGewp

Member
Messages
73
Reaction score
1
Points
8
Location
Washington County, OR
You could have stacked your fixtures like you had in your original drawing. Either way code says you need a 2" drain.

The tee and below is 2". The vent and the drain/trap arm currently connected is 1.5 from a bathtub.

So if i CAN stack them like in my "drawing", both santees need to be 2"? Does it matter if the shower or the tub is on top? Thanks!
 

James Henry

In the Trades
Messages
1,579
Reaction score
404
Points
83
Location
Billings, Montana.
Both San-tees need to be 2" because one is a vent for the other. if you want super fast drains use 2" p-traps and drains on both. I would put the shower on top. What you have is a common vent / vertical wet vent. Perfectly legal.
 

TheGewp

Member
Messages
73
Reaction score
1
Points
8
Location
Washington County, OR
Both San-tees need to be 2" because one is a vent for the other. if you want super fast drains use 2" p-traps and drains on both. I would put the shower on top. What you have is a common vent / vertical wet vent. Perfectly legal.

Finally got to it. Used a T-Waste drain on the tub and it can now handle the full flow from the faucet.

2020-02-12 18.14.49-1.jpg
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks