ALL
I have installed my 2 - 20 amp appliance circuits, and I am ready to install my recepticles. The only 20 amp recepticles that I have been able to find have one of the blade slots at 90 degrees to the other. What is confusing me is my other house which is only 9 years old has the appliance recepticles that have both blade slots parallel to each other? Are these 15 amp recepticles on a 20 amp circuit.
Thanks in advance for your replys
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
When looking at the receptacle with the ground plug on the top:

A 120 Volt - 20 Amp receptacle has a vertical slot on the left and a "sideways tee" slot on the right. That receptacle will accept either a 20 Amp plug or a 15 Amp plug.

It is permissable to use the more common 15 Amp receptacle (both slots vertical) on a 20 Amp circuit.

A 240 Volt - 20 Amp receptacle has a vertical slot on the RIGHT and a horizontal slot on the LEFT. Some (example in link below) may have a tee slot on the right to accept a 15 Amp plug.

http://www.frentzandsons.com/Hardware References/plugandreceptacleconfiguratio.htm#20 Amp.
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
When looking at the receptacle with the ground plug on the top
What are everyone's thoughts about whether you should install receptacles with the ground above or below the current-carrying holes?
 

brosnt1

Member
Messages
38
Reaction score
0
Points
6
Thanks for the reply. I did not know it was allowable to use 15 amp recepticles on a 20 amp appliance circuit.
Thanks again
 

Wet_Boots

Sprinkler Guy
Messages
799
Reaction score
2
Points
16
Location
Metro NYC
When looking at the receptacle with the ground plug on the top:

A 120 Volt - 20 Amp receptacle has a vertical slot on the left and a "sideways tee" slot on the right. That receptacle will accept either a 20 Amp plug or a 15 Amp plug.

It is permissable to use the more common 15 Amp receptacle (both slots vertical) on a 20 Amp circuit.

A 240 Volt - 20 Amp receptacle has a vertical slot on the RIGHT and a horizontal slot on the LEFT. Some (example in link below) may have a tee slot on the right to accept a 15 Amp plug.

http://www.frentzandsons.com/Hardware References/plugandreceptacleconfiguratio.htm#20 Amp.
Is this so, and is there a citation for this? I was warned off of the idea of supplying 15A receptacles with more than a 15A breaker (although it was several years ago, so codes may have changed)
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Is this so, and is there a citation for this? I was warned off of the idea of supplying 15A receptacles with more than a 15A breaker (although it was several years ago, so codes may have changed)


Still the same words that they were in the 1975 code cycle

table21021B3.jpg


jwelectric-outlets.jpg
 
Last edited by a moderator:

KD

New Member
Messages
207
Reaction score
0
Points
0
If a 20 amp circuit has only one outlet--that outlet must be a 20 amp rating. Even if it is a GFCI.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
If a 20 amp circuit has only one outlet--that outlet must be a 20 amp rating. Even if it is a GFCI.

True

210.20(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.

Remember that a duplex means two therefore a duplex receptacle is two receptacles. One duplex receptacle can be installed on a 20 amp circuit.

jwelectric-outlets.jpg
 
Last edited by a moderator:
R

Rancher

Guest
What are everyone's thoughts about whether you should install receptacles with the ground above or below the current-carrying holes?
I think it's now recommended, not yet code to put the ground hole up, the reasoning being that if you have a metal face plate and it should become loose, that the first pin that it will hit is the safety ground. I think someone is spending way too much time thinking this stuff up.

I use plastic face plates in my home and have memorized that the ground pin goes down.

Rancher
 

Wet_Boots

Sprinkler Guy
Messages
799
Reaction score
2
Points
16
Location
Metro NYC
Thanks for clarifying that for me. I think I was probably looking for a 30A circuit with 15A receptacles, and was properly told it wouldn't be code. And come to think of it, could one even count on being able to use #10 wire on a standard duplex receptacle. I recall a frustrating hour spent trying to fit a 12/3 SJO cord to a mfr-supplied plug that was obviously intended for nothing larger than 14/3
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
I think it's now recommended, not yet code to put the ground hole up, the reasoning being that if you have a metal face plate and it should become loose, that the first pin that it will hit is the safety ground.
I had heard the intent was to allow any metal object (e.g., silverware in kitchens, bobby pins in bathrooms) to contact or bounce off the ground pin, rather than the hot pin if the plug and worked its way loose enough to expose the pin(s). Makes more sense than some Code items, and there are a few extension cords and appliance cords with molded plugs on them obviously designed to plug in "upside down".

I think someone is spending way too much time thinking this stuff up.
You got that right.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
While I'm not in love with the European electrical systems, I know in Germany, the plugs are designed so that they don't contact the sockets in the receptacle until they are protected (in a recess) so it is much safer inserting and removing a power plug. Instead of the sockets being just behind the faceplate, they are recessed into a depression around 1/2" deep or so.
 

SteveW

DIY Senior Member
Messages
1,282
Reaction score
22
Points
38
Location
Omaha, NE
True

210.20(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.

I must be missing something - but doesn't this seem backwards? Doesn't it imply that the single receptacle could actually be rated higher than the branch circuit it is on?
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
I must be missing something - but doesn't this seem backwards? Doesn't it imply that the single receptacle could actually be rated higher than the branch circuit it is on?


Sure does, and what would the problem be?
 
Last edited:

SteveW

DIY Senior Member
Messages
1,282
Reaction score
22
Points
38
Location
Omaha, NE
What if you have a 15 amp circuit, but put a single 20 amp receptacle on it? Seems like trouble to me!
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
What if you have a 15 amp circuit, but put a single 20 amp receptacle on it? Seems like trouble to me!


Could be troublesome for someone, but safe, the overload would open way before any damage could happen. This is no different than installing a 40 amp breaker on a 50 amp range receptacle... People just get freaked out with it comes to small appliances.
 

KD

New Member
Messages
207
Reaction score
0
Points
0
It is not OK to install a 20 amp receptacle on a 15 amp circuit. Look at the table above. It makes the user think that there is a 20 amp circuit feeding the receptacle. Same reason you do not put a 50 amp receptacle on a 30 amp circuit. Our local inspectors require a 20 amp duplex ( or single ) where a 20 amp circuit serves only one outlet.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
It is not OK to install a 20 amp receptacle on a 15 amp circuit.
This is correct
Same reason you do not put a 50 amp receptacle on a 30 amp circuit.
Again this is correct
Our local inspectors require a 20 amp duplex ( or single ) where a 20 amp circuit serves only one outlet.
Here the inspector is incorrect and I would buck him/her very hard. The local inspector can not require anything that is not in the adopted codes and to make up his/her own rules is a very good way to find their self in the unemployment line.
 

Frenchie

Jack of all trades
Messages
1,239
Reaction score
0
Points
36
Location
Brooklyn, NY and Fire Island, NY
It is not OK to install a 20 amp receptacle on a 15 amp circuit. Look at the table above. It makes the user think that there is a 20 amp circuit feeding the receptacle. Same reason you do not put a 50 amp receptacle on a 30 amp circuit. Our local inspectors require a 20 amp duplex ( or single ) where a 20 amp circuit serves only one outlet.

But you can put a 50-amp receptacle on a 40-amp circuit... sometimes I wonder about code logic.

While I'm not in love with the European electrical systems, I know in Germany, the plugs are designed so that they don't contact the sockets in the receptacle until they are protected (in a recess) so it is much safer inserting and removing a power plug. Instead of the sockets being just behind the faceplate, they are recessed into a depression around 1/2" deep or so.

Are those like the recessed receptacles we have here, for behind wall clocks or flatscreens & etc.?
 

Attachments

  • 689w.jpg
    689w.jpg
    56.4 KB · Views: 1,409
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks