Hello all,

Does anyone see major (or minor) problems with this installation?

*Condensate drain not yet installed at time of photo. Old washing machine standpipe modified for condensate drain (2" air gap)

Thanks for playing!!

William
 

Attachments

  • tankless.jpg
    tankless.jpg
    52.6 KB · Views: 138

Breplum

Licensed plumbing contractor
Messages
1,971
Reaction score
801
Points
113
Location
San Francisco Bay Area
Condensate drain must not go directly into a plumbing system drain without an acid neutralizer kit.
https://www.supplyhouse.com/Axiom-N...iIzMQAAhrLLGhvnx-F5QbnxI2Qh1SwgQaAkEIEALw_wcB

If that is CSST, and depending on your model BTU rating, if over 10' of CSST then you may not have proper gas supply from 3/4" CSST. 3/4" CSST does not have equal capacity to 3/4" steel pipe.

Too bad you won't have a warranty: Takagi states: "8Page• Installation and service must be performed by a qualified installer (for example, a licensed plumber or gas fitter), otherwise the warranty will be void.• The installer (licensed professional) is responsible for the correct installation of the water heater and for compliance with all national, state/provincial, and local codes.• The manufacturer does not recommend installing the water heater in a pit "
 
Messages
36
Reaction score
0
Points
6
Location
Racine, Wisconsin
Neutralizer is not required in my jurisdiction. We can actually drain these just about anywhere here.

I'm not worried about warranty when I could replace the machine 4 times before paying someone else to install one for me. Call me crazy...

This unit is the 160,000 BTU/hr model. The CSST run is 8' end-to-end. Furthermore, my digital manometer indicated .1 "WC of pressure drop with all gas appliances running at max versus all turned off, so I take that to mean the supply piping is sufficient. Would you agree?

I really appreciate your comments and thanks for taking the time!!
 
Messages
36
Reaction score
0
Points
6
Location
Racine, Wisconsin
Condensate drain must not go directly into a plumbing system drain without an acid neutralizer kit.
https://www.supplyhouse.com/Axiom-N...iIzMQAAhrLLGhvnx-F5QbnxI2Qh1SwgQaAkEIEALw_wcB

If that is CSST, and depending on your model BTU rating, if over 10' of CSST then you may not have proper gas supply from 3/4" CSST. 3/4" CSST does not have equal capacity to 3/4" steel pipe.

Too bad you won't have a warranty: Takagi states: "8Page• Installation and service must be performed by a qualified installer (for example, a licensed plumber or gas fitter), otherwise the warranty will be void.• The installer (licensed professional) is responsible for the correct installation of the water heater and for compliance with all national, state/provincial, and local codes.• The manufacturer does not recommend installing the water heater in a pit "

I truly do appreciate your insights here. Upon reading further about the acidity of the condensate, I have chosen to install the neutralize you linked to. No reason to harm environment just because the code says I can... It wont interrupt the current install too badly!

Also, that last bit about the pit in the warranty statements? For full clarity, are you saying a basement install would fail regardless of who did the work? Are they considering a basement to be a pit? I suppose it fundamentally is a pit... It is very common to install these in basements here, so I am wondering if this is only Takagi? Or do they all say that?

I could really use your help on my other thread regarding my DWV pipes. Its such a mess!! I have been studying and came up with a plan, but I don't want to do all things twice (or more).
https://terrylove.com/forums/index.php?threads/first-timer-here-begging-your-expertise.93558/

Thanks again,

William
 
Last edited:
Messages
36
Reaction score
0
Points
6
Location
Racine, Wisconsin
As long as you didnt use brass pex fittings for condensate your good

To be honest, right now it is draining very close to the unit using 1/2" PVC fittings. Until I have the utility sink (laundry basin sink) setup in its new location, the condensate is directed toward the basement floor drain.

Is this because the acidic water doesn't play nice with brass? Corrosion issues? Thanks for your insights!
 

Reach4

Well-Known Member
Messages
38,905
Reaction score
4,439
Points
113
Location
IL
Messages
36
Reaction score
0
Points
6
Location
Racine, Wisconsin
This is awesome, thanks for the link!! And also really good to know about the other materials. Makes complete sense, but not something I have thought about before...
 

Fitter30

Well-Known Member
Messages
4,373
Reaction score
800
Points
113
Location
Peace valley missouri
Neutralizer is not required in my jurisdiction. We can actually drain these just about anywhere here.

I'm not worried about warranty when I could replace the machine 4 times before paying someone else to install one for me. Call me crazy...

This unit is the 160,000 BTU/hr model. The CSST run is 8' end-to-end. Furthermore, my digital manometer indicated .1 "WC of pressure drop with all gas appliances running at max versus all turned off, so I take that to mean the supply piping is sufficient. Would you agree?

I really appreciate your comments and thanks for taking the time!!
If your drain is cast iron you need a neutralizer unless after a few years you want to pay to have the line replaced.
 
Messages
36
Reaction score
0
Points
6
Location
Racine, Wisconsin
If your drain is cast iron you need a neutralizer unless after a few years you want to pay to have the line replaced.
Thanks for your input. It seems there is ecological reason to do so as well, so it will make the hippies happy!! Got to like that! Reach4 mentioned the corrosion issues, so its certainly something more serious than I would expect. I like the idea of not paying $50 for some plastic and limestone tho! I am glad Reach4 mentioned it before I purchased the one in breplumb's link!
 

Fitter30

Well-Known Member
Messages
4,373
Reaction score
800
Points
113
Location
Peace valley missouri
Thanks for your input. It seems there is ecological reason to do so as well, so it will make the hippies happy!! Got to like that! Reach4 mentioned the corrosion issues, so its certainly something more serious than I would expect. I like the idea of not paying $50 for some plastic and limestone tho! I am glad Reach4 mentioned it before I purchased the one in breplumb's link!
Could also take a five gallon plastic bucket with lid filled with chat and a bulkhead fitting mounted in side up at top of chat line. Condensate line through the top bulkhead fitting hose to drain.
 
Messages
36
Reaction score
0
Points
6
Location
Racine, Wisconsin
This seems like a much longer service interval plan! I like it!

I am in the process of relocating the laundry basin sink in my basement and would like to work more horizontally because I only have about 18" of drop from the heater outlet to the top (flood level) of the laundry basin sink. The bucket would surely eat up my available slope distance for proper drainage, and I would have to drain into the floor drain. Not to say that is a bad thing. Just trying to consider all aspects...

Maybe I could find something that could be conveniently oriented in the horizontal (slight drain slope) orientation and would work within my tight height constraints to still hit the sink instead of the floor drain...

Thank you so much for your input, I really do appreciate it!
 