Water pressure slowly -up-down and repeats

Users who are viewing this thread

JeffVee

New Member
Messages
4
Reaction score
0
Points
1
Location
Moncton NB Canada
Hi There - I’m looking for some solid advice on what my problem could be. I have a 100foot well - 20 gallon fiber woind well mate tank. I have replaced the gauge, pressure switch and repressurized the tank to 28lbs (switch is 30/50). Before swapping out the parts from above the pump would engage for about 35 seconds and then shutoff and this would repeat constantly. After swapping the new gauge and switch the cycle of cut in and cut out is about 2 minutes (2 minutes to drop from 50lbs to 30lbs- and no water was being used). At least now I know the pump is cutting in and out at the correct pressures 30/50. So I’m thinking there could be a small leak somewhere in the system - but I’m hoping someone has run across this problem and could offer some advice as to what to troubleshoot next. Thanks Jeff
 

Reach4

Well-Known Member
Messages
38,893
Reaction score
4,436
Points
113
Location
IL
Close the valve that passes water from the pressure tank to the rest of the house. This is to make sure the leak is not after that valve. If the cycling stops with that valve is closed, look for a leak downstream of the valve.

So there is a leak. Presuming that you have a pitless adapter, you can open the well cap, and listen when it is quiet. Some leaks could be hearable from the top of the casing. Most are not, but it is easy to check. If in doubt, borrow some younger ears.

You could have an underground leak. Your check valve could be leaking. The O-ring on the pitless attachment could be leaking. Pumps have a check valve built in, and/or there is a check valve placed right above the pump.
 

JeffVee

New Member
Messages
4
Reaction score
0
Points
1
Location
Moncton NB Canada
Close the valve that passes water from the pressure tank to the rest of the house. This is to make sure the leak is not after that valve. If the cycling stops with that valve is closed, look for a leak downstream of the valve.

So there is a leak. Presuming that you have a pitless adapter, you can open the well cap, and listen when it is quiet. Some leaks could be hearable from the top of the casing. Most are not, but it is easy to check. If in doubt, borrow some younger ears.

You could have an underground leak. Your check valve could be leaking. The O-ring on the pitless attachment could be leaking. Pumps have a check valve built in, and/or there is a check valve placed right above the pump.
Thanks reach4 ! I’ll be trying your suggestions this weekend, will let everyone know what problem is.
 

JeffVee

New Member
Messages
4
Reaction score
0
Points
1
Location
Moncton NB Canada
Ok back at the cottage this weekend - pressurized the tank and shut off the water valve coming in from the well. Still cycling from 50 to 30 amd repeats. Newbie question before I start crawling under the cottage lookong gor a leak. Should the water tank pressure go up amd down basically mimicking the pressure gauge?
 