meeotch
New Member
I just had my 40 gal water heater replaced. On its first heating cycle, the pressure release line squirted out 1-2 cups of water. I opened the manual, and on page 6 was a giant warning about thermal expansion tanks being required in the presence of a backflow preventer (which my building does have). I called a couple plumbers, including the one who installed the new heater, and was told, "Thermal expansion tanks generally aren't installed, especially for a small tank like that."
Bought a pressure gauge, and got the following results:
The tank is under a staircase in a storage area, space is limited, and the tank connections are already a bit of a copper knot, due to the hot/cold supply lines being installed backwards (hot on the right, cold on the left) by a previous plumber. So installation of a TE tank at the water heater is not ideal.
Question #1: Am I correct that the TE tank can be anywhere in the system, and that it can be connected with flexible hose (this is NYC)? Specifically, I'd like to put it under the kitchen sink, and connect it to the braided flex hose that feeds the cold water to the faucet. It seems like this would be simple enough that I could do it myself, no soldering.
---------------
Separate issue: I get water hammer whenever I turn off the taps (not while running). The sound doesn't bother me, but I'm concerned about stress it may by putting on the system.
The domestic system goes roughly like this: street -> backflow preventer -> water heater -> bathroom sink -> toilet -> kitchen sink. (No dishwasher.)
Question #2: Is it correct that water hammer arrestors need to be placed between the supply and the fixtures? The only exposed pipe that's upstream of both sinks & toilet is at the water heater. The other available location is at the "end of the line" under the kitchen sink. (Is it possible to install an arrestor on flexible hose, under the sink - and will that protect against hammer from the other fixtures?)
Question #3: Will the thermal expansion tank serve the same purpose as a hammer arrestor for the cold line, if placed at the water heater supply, rather than under the kitchen sink? Or are they different animals, and I really need both?
----------------
Of course, I can consult a local plumber for expert advice on these issues. But as you might gather from the above, I've already fallen into a situation where the local experts don't seem to be following best practices.
UPDATE: I should mention that there's probably only 30-40' of total pipe between all of the fixtures. 10' from the heater to the bath sink, then 10' to the toilet, then 10' to the kitchen sink. Unfortunately, all of it is behind drywall except a short tangled section of copper between the heater and its feeds, and then the flexible part under the kitchen sink. (Bath sink flex hose is exposed, and it would be ugly to install anything there.)
I've added a photo of the under-sink area. The plan would be to install a tee on the cold flexible hose, and stash the TE tank in the corner.
Bought a pressure gauge, and got the following results:
- House pressure was ~45 psi "at rest" - seems good to me
- Tank pressure after taking a 5-10 min shower rose to ~65 psi about 10 min afterward - obviously thermal expansion, but it seems within acceptable limits. (Google says 80+ psi is dangerous.)
- Ran the hot until it went lukewarm. Tank pressure rose to 150 psi over the course of an hour, then the relief valve squirted out a small amount of water.
The tank is under a staircase in a storage area, space is limited, and the tank connections are already a bit of a copper knot, due to the hot/cold supply lines being installed backwards (hot on the right, cold on the left) by a previous plumber. So installation of a TE tank at the water heater is not ideal.
Question #1: Am I correct that the TE tank can be anywhere in the system, and that it can be connected with flexible hose (this is NYC)? Specifically, I'd like to put it under the kitchen sink, and connect it to the braided flex hose that feeds the cold water to the faucet. It seems like this would be simple enough that I could do it myself, no soldering.
---------------
Separate issue: I get water hammer whenever I turn off the taps (not while running). The sound doesn't bother me, but I'm concerned about stress it may by putting on the system.
The domestic system goes roughly like this: street -> backflow preventer -> water heater -> bathroom sink -> toilet -> kitchen sink. (No dishwasher.)
Question #2: Is it correct that water hammer arrestors need to be placed between the supply and the fixtures? The only exposed pipe that's upstream of both sinks & toilet is at the water heater. The other available location is at the "end of the line" under the kitchen sink. (Is it possible to install an arrestor on flexible hose, under the sink - and will that protect against hammer from the other fixtures?)
Question #3: Will the thermal expansion tank serve the same purpose as a hammer arrestor for the cold line, if placed at the water heater supply, rather than under the kitchen sink? Or are they different animals, and I really need both?
----------------
Of course, I can consult a local plumber for expert advice on these issues. But as you might gather from the above, I've already fallen into a situation where the local experts don't seem to be following best practices.
UPDATE: I should mention that there's probably only 30-40' of total pipe between all of the fixtures. 10' from the heater to the bath sink, then 10' to the toilet, then 10' to the kitchen sink. Unfortunately, all of it is behind drywall except a short tangled section of copper between the heater and its feeds, and then the flexible part under the kitchen sink. (Bath sink flex hose is exposed, and it would be ugly to install anything there.)
I've added a photo of the under-sink area. The plan would be to install a tee on the cold flexible hose, and stash the TE tank in the corner.
Last edited: