    I have a Hunter I-Core controller with 15 zones active. A few of the zones share a field wire and use Add-a-Zone modules, but zones 1 and 2 appear to be wired direct, that is each has its own wire running from the controller to the solenoid.

    Recently, the system has begun acting like the wires for zones 1 and 2 are shorted. That is, whenever the controller calls for either zone 1 or zone 2 to be active, both solenoids come on. An irrigation "expert" told me that this can sometimes be cause not by shorted wires, but by a faulty solenoid. I don't see how that could be the case, unless a bad solenoid can cause the controller to energizer another zone.

    Anyone run into this before? Any thoughts? Thanks!
     
  2. WorthFlorida

    WorthFlorida The wife is still training me.

    Joined:
    Oct 28, 2009
    Occupation:
    Retired
    Location:
    Orlando, Florida
    Remove both wires to these two solenoids and activate each zone. With a voltmeter you may see 24 v ac on both zones when just one is activated. This Hunter unit can handle two zones at the same time. If you have no spare zones just adjust the timer for these two zones with no time set for zone 2, and you have enough pressure to run both at the same time. Or replace the first module for zones 1-6. Swapping it with another module the problem should follow the module.

    Your so called expert is good with false non sense information or just to see how you react. A shorted solenoid may have damage the plug in module but this I-Core has a short detection and it shuts down that zone. A solenoid is good or bad, no much in between.

    https://www.sprinklerwarehouse.com/amfile/file/download/file_id/10586/product_id/28629/
    The Hunter Quick Check is an efficient and effective way to diagnose problems in the field. Instead of having to physically check each field wiring circuit for potential problems, the user can run the Hunter Quick Check circuit test procedure. This circuit diagnostic procedure is very beneficial to quickly identify “shorts” commonly caused by faulty solenoids or when a bare common wire touches a bare station control wire.

    To initiate Hunter Quick Check: With the dial in the RUN position, press and hold the +, –, ◄ or ► buttons for approximately two seconds and then release.
     
    Last edited: Mar 10, 2020
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. Nelcoa

    Nelcoa New Member

    Joined:
    Mar 6, 2020
    Location:
    Houston, TX

    Thanks for the suggestions. The hunter unit checks out OK, so I guess I am left with the unpleasant prospect that the wires are actually shorted somewhere underground. Not looking forward to dealing with that...
     
  5. Nelcoa

    Nelcoa New Member

    Joined:
    Mar 6, 2020
    Location:
    Houston, TX
    ...or I guess I could just live with the short and regard the current #1 and #2 zone wires as a single wire and use Add-a-zones on the solenoids... (there’s not enough pressure to run zone 1 and 2 at the same time)
     
Similar Threads: Shorted zones
Forum Title Date
Irrigation / Sprinkler Forum Almost no pressure in 4 out of 6 zones Aug 16, 2020
Irrigation / Sprinkler Forum Sprinkler Zones Won’t Respond Jul 20, 2020
Irrigation / Sprinkler Forum Two zones on one valve Apr 20, 2020
Irrigation / Sprinkler Forum Multiple Zones on 1 Valve Apr 20, 2020
Irrigation / Sprinkler Forum KRain Pro EX switching Zones Jun 15, 2018

Share This Page