I replaced my well pump 11 years ago. A few weeks ago it tripped the breaker and blew a fuse on one leg of the cut off switch. Replaced fuse and reset breaker and it was good for a week.
Tripped breaker again and wouldn't come back on.
I checked voltage to top of well head, all around 120, but only 1.9 amps power draw. Assumed pump was bad and pulled it. Checked resistance on all wires going down well and they were at .5 or so ohms max. They tested it at plumbing house and while it had good pressure barely had any flow. It is a 3 wire 3/4 hp 7gpm sand handler set at about 150' and about 150' from the house. We figured it just wasn't pumping enough flow to get to house and it was worn out, so I grabbed a replacement. Install pump and still have no water and still about a 1.5 to 2 amp draw.
I have bypassed the cut off switch and pressure switch as well as taken the motor controller to the plumbing house to test it (good) and am at the end of my rope. I also checked resistance of wires going from house to well. Those were fine.
I am going to pull pump tomorrow and replace wires from house to well head as well as to the pump. I also plan on replacing pressure switch, motor controller, and the lines running from circuit box to pressure switch and everything in between. I'm at the point of scorched earth and replacing everything unless someone tells me different.
I figure that a wire is corroded and still making contact so there is low resistance but it is not in good enough condition to pass full amperage. Any other ideas before I start ripping stuff out of the ground again?
Tripped breaker again and wouldn't come back on.
I checked voltage to top of well head, all around 120, but only 1.9 amps power draw. Assumed pump was bad and pulled it. Checked resistance on all wires going down well and they were at .5 or so ohms max. They tested it at plumbing house and while it had good pressure barely had any flow. It is a 3 wire 3/4 hp 7gpm sand handler set at about 150' and about 150' from the house. We figured it just wasn't pumping enough flow to get to house and it was worn out, so I grabbed a replacement. Install pump and still have no water and still about a 1.5 to 2 amp draw.
I have bypassed the cut off switch and pressure switch as well as taken the motor controller to the plumbing house to test it (good) and am at the end of my rope. I also checked resistance of wires going from house to well. Those were fine.
I am going to pull pump tomorrow and replace wires from house to well head as well as to the pump. I also plan on replacing pressure switch, motor controller, and the lines running from circuit box to pressure switch and everything in between. I'm at the point of scorched earth and replacing everything unless someone tells me different.
I figure that a wire is corroded and still making contact so there is low resistance but it is not in good enough condition to pass full amperage. Any other ideas before I start ripping stuff out of the ground again?