This was from my reddit post, but I am not getting any responses so hopefully I can find some help here!
Here is the original post for my water boiler (Utica Boiler Model number MGB-100J):
In the summer I removed a radiator from my house in order to reinstall flooring. I refilled the system and then bled the radiators from top to bottom. After air came out of all but one radiator at the 2nd floor of the house, I realized that I needed I needed to repressurize the system to 12 psi (from the instruction manual guidance). I used the lever (pink arrow) on the pressure reducing valve to fill the system up to 12 psi and then pushed it down just until I no longer heard water flowing. I re-bled the system and water came out of all the radiators. I had run the boiler 3 times for about 40 Mins before realizing that the i needed to set the pressure. Since setting the pressure I have run the heat 4 times for a least an hour per time and then today for about 3 hours. When I went to the basement to check the furnace the pressure relief valve was leaking water to I immediately turned off the heat and the boiler. About 1 gallon of water came out when it was totally done dripping and the pressure went back to zero. While the water was dripping into the bucket I pushed the lever on the pressure reducing valve down in the event that it might let some pressure out. It didn't do anything so I put it back to where it originally was. The pressure gauge (after calling utica boilers they said this is not the original one) has 2 sets of numbers on it and I've been using the top set of blue numbers (blue arrow) (between 0 and 20) when I set the PSI. My question is- do I need to repressurize the system or should I let it cool and see if it will run since the excess water drained out of it or should I re-bleed and then repressurize the system to maybe a lower number? Thank you for your help!
Update:
Below is the recommended course of that was suggested to me and I did all of the steps:
Here is the original post for my water boiler (Utica Boiler Model number MGB-100J):
In the summer I removed a radiator from my house in order to reinstall flooring. I refilled the system and then bled the radiators from top to bottom. After air came out of all but one radiator at the 2nd floor of the house, I realized that I needed I needed to repressurize the system to 12 psi (from the instruction manual guidance). I used the lever (pink arrow) on the pressure reducing valve to fill the system up to 12 psi and then pushed it down just until I no longer heard water flowing. I re-bled the system and water came out of all the radiators. I had run the boiler 3 times for about 40 Mins before realizing that the i needed to set the pressure. Since setting the pressure I have run the heat 4 times for a least an hour per time and then today for about 3 hours. When I went to the basement to check the furnace the pressure relief valve was leaking water to I immediately turned off the heat and the boiler. About 1 gallon of water came out when it was totally done dripping and the pressure went back to zero. While the water was dripping into the bucket I pushed the lever on the pressure reducing valve down in the event that it might let some pressure out. It didn't do anything so I put it back to where it originally was. The pressure gauge (after calling utica boilers they said this is not the original one) has 2 sets of numbers on it and I've been using the top set of blue numbers (blue arrow) (between 0 and 20) when I set the PSI. My question is- do I need to repressurize the system or should I let it cool and see if it will run since the excess water drained out of it or should I re-bleed and then repressurize the system to maybe a lower number? Thank you for your help!
Update:
Below is the recommended course of that was suggested to me and I did all of the steps:
- Remove all water pressure.
- Check expansion tank bladder pressure and make sure it’s 15psi. Add/remove pressure so it’s 15psi. Replace if unable to do this.
- Pressurize the system again using the auto feed (pink arrow). Make sure it raises pressure to 15psi. Adjust the nut on top to achieve 15psi. If unable to do this, replace the auto feed valve. Do not add by moving the lever.
- Bleed the radiators.
- Turn the heat on.
- Monitor pressure. If relief drips while below its pressure set point (on its tag), replace the relief.