Parallel drain system for greywater - pipe sizing
AdamPNW
Washington
Hi all. DIY installer of a greywater DWV system in Bainbridge Island (UPC). Iso drawing attached. Im trying to size the greywater to a 2” drain pipe since the recommended 3-way pool valves are 2” (And it seems 3” 3-way valves would be prohibitively expensive). Diverter valves to an approved septic system are required here.
The problem is when the 2” greywater drain becomes horizontal, it no longer can accommodate 14 DFU, per code. Can a 2” drain pipe be split into two 2” pipes before it becomes horizontal? of course, then each section would need to be diverted, but possibly this is preferred over a large 3” diverter. Thoughts?
thanks, Adam
JoeJee
HVAC Contractor
Arkansas
Yes, you can split it up and have two separate lines that tie into the 3” assuming all else meets code. I don’t know how restrictive those valves are for DWV non-pressure so can’t say if your idea is good or not.
if you are talking about taking a single 2 inch drain line on the down hill side splitting it to 2 no you cant
wwhitney
Berkeley, CA
No, you can't do that.
What you can do is to avoid creating a vertical 2" pipe with more than 8 DFUs in the first place, by keeping the fixtures separate. So you'd have two parallel vertical 2" drains, each with no more than 8 DFUs.
Cheers, Wayne
John Gayewski
Iowa
You can definitely split the two sections and keep them seperate until after your diverter.
This is not a thing I've dug into. I'm not sure a pool diverter valve is OK for this. I'm actually questioning any type of system that diverts drainage. As the code has sections that would contradict the possibility of diverting. If the system needed changed later I don't think valves are a feasible way to merge a gravity drainage system. A pumped system could divert and re-divert sure, but gravity systems generally (at least in the past) aren't for changing back and fourth.
wwhitney
Berkeley, CA
John Gayewski
Iowa