Im putting a new furnace in 100,000 btu. Only place to run exhaust is 50 feet away. Its 3 inch. They ask for 1/4 inch slope. Can I get away with 8" slope for the 50 feet.
 

WorthFlorida

Clinical Trail 5th session completed 4/24/24.
Messages
5,763
Solutions
1
Reaction score
998
Points
113
Location
Orlando, Florida
Nope. What is the brand and model? Do you need both combustible outside air and exhaust? What type of vent and manufacture for the exhaust system? At 50 ft it’s a 12.5” rise. Can you lower the furnace any?
 