Hi. We have 4 yr old house with a 80 gal HTP Phoenix gas hot water (the 160,000 BTU unit) and a backup HTP electric hot water heater (with the valves closed, so it's not part of this issue). The heater is set to run at 145 degrees, and it's output is connected to a Watts LFN170-M3 Commercial water tempering valve, to try and keep the hot water temps in the house at 120 degrees or so and extend the 80 gallon hot water supply. The house also has a hot water recirculation system, using a Bell and Gossett NBF-22U pump (that is controlled by an automation system, so it be programmed to turn on and off at certain times or conditions). The mechanical room that contains this equipment is on one side of a large 2 story house with basement, so it's a long way to the far side of the loop.
Here are some pics of the setup:
In the last few months, we have experienced occasional cold showers, which should not be happening. They did not happen before the last 6 months. I am an engineer, and have temp sensors wired into various parts of the piping, including the gas heater input, gas heater output and tempering valve output. I also have a water flow sensor, so I can tell how much water is being used. Unfortunately I only keep about 3 months of data around, so I can't compare this to when the house was built.
Here is a chart of what the temp sensors showed this morning, and a cold shower was experienced at the opposite end of the house at approx 9 AM, and also at around 2:30 PM at a different shower in the house:
At 9 AM, you can see the hot water output temp crash, and the mixing valve (the Watts tempering valve) output being even colder. At 2:30 PM, the mixing valve output also crashes, but the hot water output of the stays above 120 degrees. Now, this doesn't make much sense, because only about 20 gallons or so of water is being consumed in that shower (I think it was the only hot water consumed at that time) at 9 AM. At 2:30, multiple showers were going on, and a lot more hot water was being used, but the hot water output didn't crash, but the mixing valve temp dropped significantly.
The HTP should not be running out of hot water for just 20 gallons of use!
Now, the recirc valve is switched on between 6 AM and 11 PM. If it is shut off, the hot water in parts of the house turn cold. Now, you will notice that in the plumbing, there don't seem to have any heat traps. In factor, the output of the recirc pump comes in near the input of the tempering valve, and the valve was hot all the time. The specs for the valve say the water should be between 40-80 degrees F, so I had a new plumber come in an look at this, and he knew nothing about "heat traps", but he installed a backflow preventer valve just after the recirc pump line output into the cold. This should prevent hot water from going to the input of the tempering valve. However the part of the pipe past the backflow preventer still seems to get still seems to get hot from time to time.
Does anyone know what could be causing this problem?
Thanks!
Mike
Here are some pics of the setup:
In the last few months, we have experienced occasional cold showers, which should not be happening. They did not happen before the last 6 months. I am an engineer, and have temp sensors wired into various parts of the piping, including the gas heater input, gas heater output and tempering valve output. I also have a water flow sensor, so I can tell how much water is being used. Unfortunately I only keep about 3 months of data around, so I can't compare this to when the house was built.
Here is a chart of what the temp sensors showed this morning, and a cold shower was experienced at the opposite end of the house at approx 9 AM, and also at around 2:30 PM at a different shower in the house:
At 9 AM, you can see the hot water output temp crash, and the mixing valve (the Watts tempering valve) output being even colder. At 2:30 PM, the mixing valve output also crashes, but the hot water output of the stays above 120 degrees. Now, this doesn't make much sense, because only about 20 gallons or so of water is being consumed in that shower (I think it was the only hot water consumed at that time) at 9 AM. At 2:30, multiple showers were going on, and a lot more hot water was being used, but the hot water output didn't crash, but the mixing valve temp dropped significantly.
The HTP should not be running out of hot water for just 20 gallons of use!
Now, the recirc valve is switched on between 6 AM and 11 PM. If it is shut off, the hot water in parts of the house turn cold. Now, you will notice that in the plumbing, there don't seem to have any heat traps. In factor, the output of the recirc pump comes in near the input of the tempering valve, and the valve was hot all the time. The specs for the valve say the water should be between 40-80 degrees F, so I had a new plumber come in an look at this, and he knew nothing about "heat traps", but he installed a backflow preventer valve just after the recirc pump line output into the cold. This should prevent hot water from going to the input of the tempering valve. However the part of the pipe past the backflow preventer still seems to get still seems to get hot from time to time.
Does anyone know what could be causing this problem?
Thanks!
Mike